This was one of my previous queries. Touch voltage is now 25 volt as per SANS 10142-1:2020. Edition 3.
This tables with the reduced ohm values is due to this lower touch voltage.
You will find it at 8.6.5.4 of the code mentioned above. 25 volt touch voltage under short circuiting conditions not exceeding a period of 5 seconds.
Thanks
Gerhard
This tables with the reduced ohm values is due to this lower touch voltage.
You will find it at 8.6.5.4 of the code mentioned above. 25 volt touch voltage under short circuiting conditions not exceeding a period of 5 seconds.
Thanks
Gerhard