Zdb / E loop and Psc on sub DB under ELU

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #1

    Zdb / E loop and Psc on sub DB under ELU

    Hello

    Wondering how to test a sub DB which is fed from Main DB but under and ELU ?

    The moment I test E loop it trips the ELU. We don't have the fancy tester that blinds the ELU so wondering how else to test it ?

    I have just been told to make a note of it and that's that but once more I want to dig deeper....

    So for the Eloop can I just measure the resistance of the Earth from main DB to Sub DB and then the restiance of the phase and then add together to make a" loop " and then do the Rmax = V / 2 x I to then make sure it can trip the CB that feeds it?



    Sent from my SM-N960F using Tapatalk
  • Dave A
    Site Caretaker

    • May 2006
    • 22812

    #2
    Bridge the top terminal to the bottom terminal for each phase and neutral of the earth leakage unit with housewire (10mm is great for a typical home installation) as a temporary bypass measure just for the purpose of the test.
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • Dylboy
      Gold Member

      • Jun 2020
      • 777

      #3
      Originally posted by Dave A
      Bridge the top terminal to the bottom terminal for each phase and neutral of the earth leakage unit with housewire (10mm is great for a typical home installation) as a temporary bypass measure just for the purpose of the test.
      Perfect, thank you. A lot simpler than what I had in mind... Will make up some nice leads for it, some panel flex 10mm.

      I see on the Internet the UK sparks are using the R2 lead thing that has a pozi bit magnet joined with a cable to a Croc clip to do the shorting... Will experiment with that idea.

      Thanks Dave!

      Sent from my SM-N960F using Tapatalk

      Comment

      • ians
        Diamond Member

        • Apr 2010
        • 3943

        #4
        If you plan to do testing in the future ... spend the money and buy a decent multifunction tester ... like mA current clamp ... once you have one ... it makes testing a breeze ... fault finding becomes a pleasure rather than a mission.

        Things like loop impendence tests at the socket outlet ... especially if you cant switch off the power ... suddenly a breeze and you can verify the wiring and etc is correct.

        I had to do testing at a school today ... I couldn't switch off the power .. .got all the test results I needed and gone without them even knowing I was there ... no need for a pieces of paper and a pen to record shyte.

        Test ... save ... next ... back to my cool office ... download and sent.

        Another advantage is the test results can be saved for future reference ...

        I believe it should be law that every inspector has a multifunction tester with a GPS to identify the location and the test result ... it would reduce the amount of dodgy COC's.

        In fact an owner of a property or person renting a property ... being the "responsible person" ... I would insist that the test results are recorded ... photos attached with the location and time stamp.
        Comments are based on opinion...not always facts....that's why people use an alias.

        Comment

        • Dylboy
          Gold Member

          • Jun 2020
          • 777

          #5
          Ians i a 100% agree with you ! I want an MFT with the no trip especially for the reason of sage live testing.

          Liek your job of the school that is perfect, we often did commercial buildings and no matter how much planning goes on someone is effed off the power is out....

          I have my eyes in a couple from the UK... just need to finalise some things here and then save for that.

          Even the Miliamp meter... I have a few i want but for starters have a cheaper one that has good reviews in my basket ready to order...
          Can not wait for either.


          If you need a 10mm hole but only a 1mm drill bit you in for a long time.... but a 10mm drill bit it is quick... the right tool for the job....

          Sent from my SM-N960F using Tapatalk

          Comment

          • ians
            Diamond Member

            • Apr 2010
            • 3943

            #6
            When I was bass fishing ... a gloomis fishing rod and Callais DC reels was expensive ... I believe you need the right tools for the job ... my goal was to win the season in our province ... I got a credit card and used it specifically for the tackle I needed ... and paid it off over a period of time ... then closed the credit card and cut it up ... I found a partner who was just as dedicated to winning ... we achieved our goal and won the season with a bag average of over 8 kg for the season ... I caught more than 50 x 2kg bass and more 30 x 3 kg bass in one season.

            So if you are serious about your job and want to be the best at it what you do ... make sure you have the right equipment to achieve your goal ... get rid of that expensive phone and contract get cheap transport and focus on what pays the bills.

            Dont make mistakes like I have and go over board ... by buying fluke 435 and top of the range thermal imagers ... unless of course that is what you are going to focus on.

            I may drive an old scrap vehicle ... but when it comes to my work ... I have equipment in my business is worth more than my house ... at the end of the day it shows in the quality of my workmanship and attention to detail which results in return customers and no need to advertise ... every single job I do is from word of mouth.

            If I need to chase a wall without dust I have the right equipment ... if I need to work 14 ft in the air ... I have the ladders and scaffolding to do the job .. .you get the idea.
            Comments are based on opinion...not always facts....that's why people use an alias.

            Comment

            • Dylboy
              Gold Member

              • Jun 2020
              • 777

              #7
              I agree so much with all you said there, I am slowly building up the arsenal, I mostly now only get the specialist tool when required for a job as been cought out before preempting a purchase for a job that then falls through and cashflow a bit shot then, but when you use that tool once and makes what would have been a 30 min job a 5 min one it is so so worth it and if not double worth it haha.



              Sent from my SM-N960F using Tapatalk

              Comment

              • Pieter00
                Bronze Member
                • Mar 2013
                • 112

                #8
                What’s the make and model of this tester?

                Comment

                • ians
                  Diamond Member

                  • Apr 2010
                  • 3943

                  #9
                  There are a couple of different brands ... my personal choice is fluke ... the guys at comtest have grown over the years and the guys working there have have many years of experience ... so the support is good ... but more important the quality and safety is the best in my experience. Some of my testers are obsolete and still work 100%

                  Megger is punting their multi function tester ... but I dont have any experience with the product.

                  Major tech have a multi function tester ... but unless it has a K in front of the model number ... I wouldnt use it for anything more that testing batteries in my workshop.

                  Metrel also make a good product ... I have a power quality analyser and it is pretty robust ... they also do a multi function tester.
                  Comments are based on opinion...not always facts....that's why people use an alias.

                  Comment

                  • Dylboy
                    Gold Member

                    • Jun 2020
                    • 777

                    #10
                    If I can I would get the megger or fluke.

                    How ever I am looking at the TIS MFT and then the Metrel as well.

                    I have a metrel voltage tester and love that.

                    Reason for metrel and the TIS are the price points ans reviews of them for the MFT.

                    I only look at getting from the UK due to price but I do not know of after service repairs in SA....

                    Sent from my SM-N960F using Tapatalk

                    Comment

                    • ians
                      Diamond Member

                      • Apr 2010
                      • 3943

                      #11
                      From my experience with Fluke products ... after sales service is not required ... it just works ... however sometimes with the more advanced equipment ... having a person who can assist with technical setup and operation is a huge help.


                      I have also been watching the TIS MFT ... Dave Savery electrical punts it on youtube.

                      Personal I stick with brands I trust ... unfortunately in some cases like Hilti ... they make a really good quality product ... their support for small business is non existent or should I say they dont give a rats a$$ about the little guy ... so you have to decide if you are prepared to pay 10 times the price of other brands for a disposable product ... or buy though a company with a lot of employees which will result in a massive discount ... Hilti discount structure works on employee count not quantity of purchase ... how do I know this ... I sub contract to big companies and get to purchase huge volumes of product for specific sites ... if you knew how bad you get screwed as a company with few employees ... you would probably not support Hilti out of principle ... It is so sad.

                      When you buy equipment for R50 000.00 or R100 000.00... the difference between the 10 % discount and 45 % makes you pay attention ...so much so that the 15 % vat makes your 10 % discount seem silly.
                      Comments are based on opinion...not always facts....that's why people use an alias.

                      Comment

                      • Dylboy
                        Gold Member

                        • Jun 2020
                        • 777

                        #12
                        Yes ya it was David Savery that first got me looking into the Metrel and then the TIS. Then a few other sparks have spoken of or used the TIS so it is a heavy contender for me especially at the price.

                        And sorry about the Hilti not honouring what it said and hiding behind fine print. I do think their tools are one of and if not the best but If they give the small guy the run around then not keen... but also as devils advocate I have not had to deal with any other brand as yet with warranty so maybe they also up to sh!t.

                        I am a fan of the dewalts, Makitas, Fest tool and the like as they are mid way on price and the performance is kind of there.



                        Sent from my SM-N960F using Tapatalk

                        Comment

                        • ians
                          Diamond Member

                          • Apr 2010
                          • 3943

                          #13
                          Once you have been hands on working with equipment for as long as I have ... you learn which tools are the best for the application.

                          For example I still have matabo machines from when I started the business 31 years ago ... I found for steel work metabo would be my first choice.

                          Brick and concrete ... Hilti would be my first choice ... even though the support for the product in SA for small business is so crap ... the machine quality is still the best.

                          Wood work ... festool if you can afford it ... other wise Makita makes a really good product ... all my woodworking machines are Makita

                          A good example of unsuitable combinations ... 15 minutes using the Hilti vacuum in the workshop connected to the drum sander and ... the Hilti machine stalls ... the makita vacuum will run until it is full.

                          Yet if I use the makita vacuum on site with the dustless chasers ... 3 days and the motor is %^&* ... the Hilti just keeps going.

                          Another example using a TE 55 for chipping walls ... bad idea ... yet you can drill 30 mm holes through concrete floors ... all day long ... I have a small makita breaker .... we use it for shipping walls ... it can run all day.

                          When it comes to test equipment ... fluke wins hands down ... It's is too dangerous to use other tester ... I feel confident putting my hands in a 1500 amp DB using a fluke test ... I would wear rubber gloves with leather gloves over them if I were to use any other make of tester. Yes I have made that mistake of forgetting to change the leads ... all you hear is small pop sound and the fuse blows inside the meter.

                          The fluke test leads dont last long but compared to other test leads ... I would rather get the fluke ones.
                          Comments are based on opinion...not always facts....that's why people use an alias.

                          Comment

                          Working...