Pool pump DB, fixed appliance or sub DB

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Dave A
    Site Caretaker

    • May 2006
    • 22810

    #16
    Originally posted by GCE
    In my opinion the isolator would need to be at the control box in the event of removal
    The pool guy is not a electrician and will be the one working on the appliance.
    Will he always be able to access the DB when he comes to carry out repairs ?

    Could reg below come into play ,


    6.16.5.1.4 Each motor shall be supplied by a manually operated disconnector
    or any other manually operated disconnecting arrangement such as a
    withdrawable circuit-breaker, a removable link, a fuse or by the removal of a
    plug from a socket-outlet, which provides at least the same isolating distance,
    for the sake of safety, as a disconnector that is
    a) readily accessible and mounted on or next to the motor, or
    b) visible from the motor, or
    c) lockable in the open position, or
    d) housed in a lockable enclosure other than a distribution board.
    Ah. The "motors" requirement for disconnecting devices. But isn't that why the pump motor is normally plugged into a socket outlet on the control panel?
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • GCE
      Platinum Member

      • Jun 2017
      • 1473

      #17
      Originally posted by Dave A
      Ah. The "motors" requirement for disconnecting devices. But isn't that why the pump motor is normally plugged into a socket outlet on the control panel?
      I have not seen that , the pump plugged in - I have seen the Pool " control box " plugged into a socket outlet

      Comment

      • Dave A
        Site Caretaker

        • May 2006
        • 22810

        #18
        I did say the "lockable isolator in DB" was a can of worms

        But they are lockable and I don't recall the SANS code saying anything about "subject to general availability of locking devices".

        My favourite article on the subject remains this one on disconnecting devices by Cecil Lancaster.
        Participation is voluntary.

        Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

        Comment

        • Dave A
          Site Caretaker

          • May 2006
          • 22810

          #19
          Originally posted by GCE
          I have not seen that , the pump plugged in - I have seen the Pool " control box " plugged into a socket outlet
          A few current options after a quick search.
          From ACDC
          From Voltex

          There's a model that's been used extensively in most domestic installations in Durban for many years. When I come across a photo of one, I must remember to post it.
          Participation is voluntary.

          Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

          Comment

          • Derlyn
            Platinum Member

            • Mar 2019
            • 1748

            #20
            I have yet to see a pool db with an isolator on the supply in close proximity to the db.

            All those that I come across are sub db's.

            I prefer it that way because I charge per db when doing an inspection. More db's .... more moola. That's why I'm there in the first place.

            Comment

            • Dave A
              Site Caretaker

              • May 2006
              • 22810

              #21
              Here's an interesting one we had to deal with recently.

              Click image for larger version

Name:	socket-outlet-for-pool- pump.jpg
Views:	1
Size:	82.0 KB
ID:	266131

              This socket outlet is under a pool pump cover and supplies the pool motor. It is on a "plugs" circuit and without doubt part of the electrical installation.
              Does it need to be in a weather resistant enclosure or is the fact that it is under a pool pump cover enough?
              Participation is voluntary.

              Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

              Comment

              • GCE
                Platinum Member

                • Jun 2017
                • 1473

                #22
                Originally posted by Dave A
                I did say the "lockable isolator in DB" was a can of worms

                But they are lockable and I don't recall the SANS code saying anything about "subject to general availability of locking devices".

                My favourite article on the subject remains this one on disconnecting devices by Cecil Lancaster.
                I have seen some bad outcomes when contractors have taken those articles to heart instead of treating them as comically , which I am sure was the intention

                The lockable argument and discussion has been had many times and I tend to agree with the AIA viewpoint that if you cant put your padlock on without extra mods then it is not lockable.

                It would be like booking into a hotel and they tell you that the door is lockable , you just need to supply your own locking mechanism , the holes are all in place for mechanism type FUT023

                Comment

                • GCE
                  Platinum Member

                  • Jun 2017
                  • 1473

                  #23
                  Originally posted by Dave A
                  A few current options after a quick search.
                  From ACDC
                  From Voltex

                  There's a model that's been used extensively in most domestic installations in Durban for many years. When I come across a photo of one, I must remember to post it.
                  Always seen those sockets just been used as a garden type socket outlet for weed eater- have not seen the pump plugged in - I am almost sure that the timer is not wire to the socket

                  Comment

                  • GCE
                    Platinum Member

                    • Jun 2017
                    • 1473

                    #24
                    Originally posted by Dave A
                    Here's an interesting one we had to deal with recently.

                    [ATTACH=CONFIG]8476[/ATTACH]

                    This socket outlet is under a pool pump cover and supplies the pool motor. It is on a "plugs" circuit and without doubt part of the electrical installation.
                    Does it need to be in a weather resistant enclosure or is the fact that it is under a pool pump cover enough?
                    I would say the socket needs to be fitted inside a weather proof enclosure that is fixed to the structure .

                    If the pool pump cover is fitted on a hinge type fitting making it a fixture like a roof that swings open then I may let it pass
                    A loose pool pump cover I would not

                    Comment

                    • ians
                      Diamond Member

                      • Apr 2010
                      • 3943

                      #25
                      Originally posted by Dave A
                      Here's an interesting one we had to deal with recently.

                      [ATTACH=CONFIG]8476[/ATTACH]

                      This socket outlet is under a pool pump cover and supplies the pool motor. It is on a "plugs" circuit and without doubt part of the electrical installation.
                      Does it need to be in a weather resistant enclosure or is the fact that it is under a pool pump cover enough?
                      I was recently told that my IP 44 rated DB was not sufficient ... because in was on the verandah under the roof out of direct sunlight at the correct height ... with a main switch and additional earth leakage protection for circuits fed from the Sub DB ... I was told by the inspector of the new owner that an IP 65 rated DB was required ... I told him to report me to the AIA.

                      So just in case I sent a picture of the location ... the DB with the frosted flap cover ... with all the blanks fitted and correct labelling (fed from ... ka rating ... feed cable size) and the drawings of the location of each circuit highlighted by circuit number and the plug and light number ... with the list of material used for each circuit ... ie : twin+E 2.5 mm buried at 500 mm in a pvc conduit below ground level protected by aluminum U channel where they surface to prevent mechanical damage by a weed eater or the like ... and a copy of the supplementary COC and test report pending the customers initial COC (which was not handed to the customer until I receive the intial) ... all to the AIA.

                      By the way the supplementary COC is no longer required because someone else did a house sale COC
                      Comments are based on opinion...not always facts....that's why people use an alias.

                      Comment

                      • Dave A
                        Site Caretaker

                        • May 2006
                        • 22810

                        #26
                        Originally posted by GCE
                        I would say the socket needs to be fitted inside a weather proof enclosure that is fixed to the structure .

                        If the pool pump cover is fitted on a hinge type fitting making it a fixture like a roof that swings open then I may let it pass
                        A loose pool pump cover I would not
                        You and I are of like mind on this one.

                        It came to my attention as a call-back from the purchaser. Her complaint was that it should be water resistant because when they backwashed the pool, there was a water leak that led to water splashing on the socket outlet. I told her that I had no duty in respect of the leak that led to the splashing, but I was uncomfortable with the socket outlet (clearly being part of the electrical installation) only being protected by the loose pool cover.

                        We put it into an Albro weatherproof box large enough to accommodate the plug-in timer at our own expense.
                        School fees...
                        Participation is voluntary.

                        Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                        Comment

                        • ians
                          Diamond Member

                          • Apr 2010
                          • 3943

                          #27
                          Originally posted by Dave A
                          Here's an interesting one we had to deal with recently.

                          [ATTACH=CONFIG]8476[/ATTACH]

                          This socket outlet is under a pool pump cover and supplies the pool motor. It is on a "plugs" circuit and without doubt part of the electrical installation.
                          Does it need to be in a weather resistant enclosure or is the fact that it is under a pool pump cover enough?
                          Today while connecting a light in a "pool" DB ... this picture got me thinking ... what is the difference between this socket outlet and an exposed socket outlet on the side of a "pool" DB?
                          Comments are based on opinion...not always facts....that's why people use an alias.

                          Comment

                          • ians
                            Diamond Member

                            • Apr 2010
                            • 3943

                            #28
                            You never too old to learn ... you read the regs with regards to a swimming pool and there is mention of zone 0 and zone 1 and 2 ... zone 1 is a vertical plane of 2 m from the rim of the basin ... however if you install a light ... you need to read the regs with regards to luminaires 7.2.4.5.1... a light cannot be within 2.5 m of the water surface.

                            This just gets a whole lot more interesting ... what about a pool pump and DB ... if referred to as a fixed appliances. I have seen small fibreglass pumps connected directly to the side of the pool.
                            Comments are based on opinion...not always facts....that's why people use an alias.

                            Comment

                            • Derlyn
                              Platinum Member

                              • Mar 2019
                              • 1748

                              #29
                              Originally posted by ians
                              I have seen small fibreglass pumps connected directly to the side of the pool.
                              They are double insulated similar to those used in aquariums and water features.

                              Comment

                              • Isetech
                                Platinum Member

                                • Mar 2022
                                • 2274

                                #30
                                Originally posted by GCE
                                The double pole as lockable in the DB without a fixed lockable device on the circuit breaker , in my opinion will not count - How does the pool guy have a CB isolator device

                                With regards to COC , it is still required under 6.16.1.10 same as a light fitting is not part of the coc but if the wiring is exposed you need to rectify , eg covers missing from fluorescent channels


                                6.16.1.10 The wiring between different parts of a fixed appliance that are
                                installed separately is part of the fixed installation, even where it is supplied
                                from a socket-outlet, unless such wiring is less than 3 m in length.
                                Such wiring shall be protected by separate overload protection unless its
                                current-carrying capacity is such that the circuit protection of the socket-outlet
                                circuit will provide protection or that part of the appliance has built-in thermal
                                overload protection.
                                NOTE Where the length of wiring exceeds 3 m, the impedance and the functioning of
                                the protective devices need to be considered to satisfy the overcurrent protection
                                requirements in this part of SANS 10142.
                                On a new install or a relocation of the pool DB, the electrician will supply the cable from the main DB to the pool DB, carry out all the tests required and issue a COC for the cable and DB.

                                There should be no need for a double pole isolator before the pool DB. The pool guy should have no reason to work in the pool DB, The pump is fitted with a plug top, which can be removed and makes it safe to work on or replace. That is why connecting a pump cable directly into a pool DB should not be allowed. He can replace the light because the light is fed from a 12 VAC safety supply. The pool guy should not be working in the pool DB for any reason. IF the circuit breaker or timer needs to be replaced, it should be done by a qualified electrician.

                                The fibre glass cover over the pool pump, changes all the rules and regs, just like a sauna. All sorts of zones apply to saunas, however as soon as you fit a cover over the electrical and controls, the zones regs no longer apply.

                                Just imagine trying to pass a pool DB installation without a cover, most pool DB's I have seen are within 3.5 m of the pool surface.

                                Adding circuits to the pool DB is no different, so long as you apply all the zone regs, the pool DB is still the pool DB/sub DB. People manipulate the regs to suit their application.

                                The same as the pic Dave posted with the socket, if the socket outlet is under the pump cover, its doesnt need to be a weather proof socket outlet. If it was not allowed than literally every pool pump installation would fail, due to the IP rating of the socket on the side of the pool DB.

                                What is important to note - The plug for the pump and anything else, like a chlorinator must have a means to remove the device without opening the DB.

                                The light can be replaced by the pool guy even if the power is not isolated, because it is fed from a safety supply.
                                Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.