As per a discussion today, what you need to understand is that the inverter is not an "online" system, it switches over from grid (at this point you cannot have a dual neutral/earth bond) to UPS (islanding mode) which is disconnected from the grid power, the reason the relay is used. For Sunsynk inverters it has a preset delay before the supply is reconnected, which is the reason it must NOT be connected directly to the mains, but rather through the contact in the inverter.
An inverter is like a cheap UPS, the grid power goes in and the grid power comes out, only when the inverter goes into islanding mode is the mains disconnected and from the mains and the DC power is converted to Ac power.
Until someone can draw a picture that doesnt show a double neutral/earth bridge on the system while the power is in grid mode, I will be connecting all the relays already installed on all the installations I have already completed. All future installation will have a relay.
This is a challenge to everyone installing inverters, what is creating the high leakage currents on installation which have a permanent bond and how dangerous is this high current.
If you do inverter installations you dont even need a leakage current detector to identify this high current, just clamp any clamp meter.
An inverter is like a cheap UPS, the grid power goes in and the grid power comes out, only when the inverter goes into islanding mode is the mains disconnected and from the mains and the DC power is converted to Ac power.
Until someone can draw a picture that doesnt show a double neutral/earth bridge on the system while the power is in grid mode, I will be connecting all the relays already installed on all the installations I have already completed. All future installation will have a relay.
This is a challenge to everyone installing inverters, what is creating the high leakage currents on installation which have a permanent bond and how dangerous is this high current.
If you do inverter installations you dont even need a leakage current detector to identify this high current, just clamp any clamp meter.