cabtyre 2 m extention max lenght
  • Gene
    • Jan 2019
    • 40
    I cannot find the regulation stating that a cabtyre extention cord needs to be max. 2 meters in lenght, so it means all extention cords longer than 2 m is not allowed in a dwelling , eg for a tv on the wall??
    • 1483
    There is no restriction on the length of an extension lead .
    If the extension lead is "fixed" into the electrical installation then that becomes a different story - Clause 6.16.1.5 or 6.16.1.10 is maybe what you were thinking of
    6.16.1.5 A socket-outlet shall supply only one fixed appliance. The use of
    flexible cords of length exceeding 3 m is not recommended. The reason for
    this recommendation is an endeavour to ensure operation of the overcurrent
    protective device. (See also 6.14.1.4 for luminaires).
    6.16.1.10 The wiring between different parts of a fixed appliance that are
    installed separately is part of the fixed installation, even where it is supplied
    from a socket-outlet, unless such wiring is less than 3 m in length