    Originally posted by Pieter00
    Should the neutral earth bridge not be done externally in an inspection type box as it's not allowed in a DB according to SANS 10142:1?[ATTACH=CONFIG]8563[/ATTACH]
    I assume they are using 7.12.3.1.3 to make that statement, that it is not allowed in the DB ? It is not so much as not allowed , just that it should be at the unit

    On bigger systems where the transformer is owned by the client , it would need to be done in the transformer room or close to it , and could be the main D/Board for the installation if that is where the main neutral earth bar is



    7.12.3.1.2 In an installation that is supplied from a combination of
    transformers and alternative supplies located near to each other, the neutral
    points of each of these items shall be connected to a single earthed neutral
    bar (see P.1 and figure P.1). This earthed neutral bar shall be the only point
    at which the neutral of the installation is earthed.
    Any earth leakage device
    shall be positioned in such a way as to avoid incorrect operation due to the
    existence of any parallel neutral/earth path.


    7.12.3.1.3 Where alternative supplies are installed remotely from the
    installation, or from one another, and where it is not possible to make use of
    a single neutral bar or neutral conductor which is earthed, the neutral of each
    unit shall be earthed at the unit
    and these points shall be bonded to the
    consumer's earth terminal (see 6.12.4). The supply from each unit which
    supplies the installation or part of the installation, shall be switched by means
    of a switch that breaks all live conductors operating substantially together
    (see figures P.2 and P.4), to disconnect the earthed neutral point from the
    installation neutral when the alternative supply is not connected (see also
    6.1.6).


    7.16.4.3 Wherever the neutral is connected to the earth, a warning notice
    shall be fitted to the outside of each distribution kiosk in the distribution
    system, indicating "Neutral earthed inside".