My assessor and I developed a difference of opinion at my assessment today.
He suggests that in a single phase installation that a single pole main disconnector that disconnects only live is sufficient?
10142 - 6.9.2.2 - "In the case of a single phase circuit, the disconnecting device shall disconnect live and neutral."
I've always replaced single pole with a double pole that disconnects both live and neutral.
Have I interpreted 10142 correctly?
He suggests that in a single phase installation that a single pole main disconnector that disconnects only live is sufficient?
10142 - 6.9.2.2 - "In the case of a single phase circuit, the disconnecting device shall disconnect live and neutral."
I've always replaced single pole with a double pole that disconnects both live and neutral.
Have I interpreted 10142 correctly?