V-O-V Generator - doing my head in!

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Andrew_van_Zyl
    Bronze Member

    • Mar 2022
    • 131

    #1

    V-O-V Generator - doing my head in!

    After brushing up on my 10142 the other day I came across a MacAfric Diesel genset that befuddles the mind - N-E 154V (Yes..read that again!) and L-E 66V. WTF!!

    Client has this connected to his DB.

    I didn't fully understand VOV until today - what is the solution? (Apart from dumping the very expensive diesel gen?)
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #2
    There are a couple of threads on this, hit the search and they should pop up.

    Some options are to disconnect the output earth of the genny and then bridge the the Neautral and the Earth going to the DB. How ever it has to be before the changeover as you can not have the permanent bridge there. Don't just bridge the Neautral and earth of the genny output as the earth is a centre tap. It you do. Ridge the centre tap you may damage the genny and basically short out half the coil.

    Some are to disconnect the earth centre tap in the genny itself too.

    But search the forum and a bunch should pop of for reading and I may have missed some stuff.. been a long day of beer...

    Sent from my CPH2197 using Tapatalk

    Comment

    • Dylboy
      Gold Member

      • Jun 2020
      • 777

      #3
      Thinking again... Use a contactor rather to make that N E bridge... Doing a perm one even at the change over at the input of the genny would still not have it disconnect when in change over so if the grid as issues it may be the N and E point for the street...

      Sent from my CPH2197 using Tapatalk

      Comment

      • Derlyn
        Platinum Member
        • Mar 2019
        • 1761

        #4
        Regarding the diesel genset, find the live and neutral wires coming from the stator, disconnect them and megger each one down to earth. If open circuit then there is not an internal connection from the main stator to earth. Ie no centre tap earth connection.

        If that is the case, one can quite safely bridge the neutral to earth on the genset. We do that regularly on genny installations.

        It is very important to first ensure that there is no centre tap earth connection before bridging anything otherwise you will be shorting out half the stator and the genny wont survive for any length of time after that.

        Comment

        • Dave A
          Site Caretaker

          • May 2006
          • 22818

          #5
          Originally posted by Dylboy
          Thinking again... Use a contactor rather to make that N E bridge... Doing a perm one even at the change over at the input of the genny would still not have it disconnect when in change over so if the grid as issues it may be the N and E point for the street...

          Sent from my CPH2197 using Tapatalk
          When on mains supply, the neutral from the generator must be disconnected from the installation as well as the live. Therefore the N to E bridge on the generator doesn't become the N to E bridge point "for the street". The generator neutral will remain connected to earth only.
          Participation is voluntary.

          Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

          Comment

          • Dylboy
            Gold Member

            • Jun 2020
            • 777

            #6
            Originally posted by Dave A
            When on mains supply, the neutral from the generator must be disconnected from the installation as well as the live. Therefore the N to E bridge on the generator doesn't become the N to E bridge point "for the street". The generator neutral will remain connected to earth only.
            Yes ya, will draw it out but surely the change over would break that Line and Neautral if genny when on Grid thus breaking the N and E of the street ?

            Sent from my CPH2197 using Tapatalk

            Comment

            • Isetech
              Platinum Member

              • Mar 2022
              • 2274

              #7
              Originally posted by Dylboy
              Yes ya, will draw it out but surely the change over would break that Line and Neautral if genny when on Grid thus breaking the N and E of the street ?

              Sent from my CPH2197 using Tapatalk
              If you wire it correctly. the neutral earth bond should be done in the changeover DB before the generator input at the changeover switch.

              Just be careful with inverters, its not the same.
              Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

              Comment

              • Dylboy
                Gold Member

                • Jun 2020
                • 777

                #8
                Originally posted by Isetech
                If you wire it correctly. the neutral earth bond should be done in the changeover DB before the generator input at the changeover switch.

                Just be careful with inverters, its not the same.
                Yes that's where I have it in my mind to do it there

                Ya inverters are different but that is where i use contactors for that.

                I mean you can buy a N E bridge box from Segen but using a contactor is the same.

                But appreciate all the input as always guys. Learning stuff everyday with this forum

                Sent from my CPH2197 using Tapatalk

                Comment

                Working...