    [Question] Inverter fault levels

    This is an interesting question, what is the fault level at the inverter when it switches over to battery backup, if you have one, 2 or 10 batteries connected.

    How do you work out the fault level when carrying out the inspection report for the COC?

    Lets say a you are using 5.2 kwh (48 VDC) batteries, in parallel.

    I am interested to see some of the calculations done by electricians who issue COC for solar installations.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.
  • Derlyn
    Platinum Member

    • Mar 2019
    • 1748

    #2
    Where on the test report would one enter those particulars ?

    Comment

    • GCE
      Platinum Member

      • Jun 2017
      • 1473

      #3
      Your Fault level on the AC output will be the max peak output of the inverter which is anywhere between 1,5 to 2 times the rating of the inverter .
      The fault level is low.

      The DC fault level internally on the inverter is a different story - With Lithium the BMS will restrict the fault current.

      With Gel it takes a bit of calculation but is generally around 12 times the Amp hr rating