    Inverter feed

    Hello

    Something not sitting too well with me and would appreciate some guidance please.

    There is an inverter that is fed from the TOP of the Main Switch, the Main Switch is an Earth Leakage.

    Now if you isolate the Main Switch the inverter DB still has power.

    The inverter DB which has a change over and stuff has a main switch for the AC in from the top of the ELU and then a CB for the out put.


    So is it ok that the Main Switch in the DB does not isolate the feed to the inverter rather the inverter DB does that isolation.

    The feed from the TOP of the Earth leakage main switch as it's CB in the inverter DB which is its main switch (double pole)

    Basically is It ok that the main DB main switch does not isolate the feed to the inverter DB ?

    Sent from my CPH2197 using Tapatalk
  • Derlyn
    Platinum Member
    • Mar 2019
    • 1761

    #2
    Nope. It's not ok. The main switch of the installation MUST isolate the WHOLE installation.

    How many times have I found this where a second dwelling ( granny flat ) has been built and then the bright spark takes the supply to the granny flat from the top of the main breaker.

    I refuse to issue a coc where I find the above.

    Comment

    • GCE
      Platinum Member
      • Jun 2017
      • 1483

      #3
      Not allowed
      Main switch must be the main switch , everything will need to be switched off - The Local main/sub main for the inverter is still needed .

      It would be similar to taking the stove point from the top of the ELU and then saying that the stove has an isolator which is the main switch - I did say similar

      Comment

      • Dylboy
        Gold Member

        • Jun 2020
        • 777

        #4
        Brilliant thanks all!

        I do agree. I always have it so that the main switch does all but this one I saw is not like that and not chuffed haha.

        Have not seen it to often so when I saw if Bells went off and searched Sans a bit on site and didn't pick up a quick obvious. Will try find the Reg and then tell the client and motivate to get it changed.



        Sent from my CPH2197 using Tapatalk

        Comment

        • GCE
          Platinum Member
          • Jun 2017
          • 1483

          #5
          Here are 2 clauses that should sort any argument


          5.3.7 Disconnecting devices
          An installation shall have disconnecting devices that allow the installation to
          be disconnected for maintenance, testing, fault detection or repair. In the case
          of circuits or items of equipment, additional disconnecting devices could be
          required to allow disconnection for maintenance, testing, fault detection or
          repair of such circuits or equipment.

          6.6.1.1 Each distribution board shall be controlled by a switch-disconnector
          (see 6.9.4). The switch-disconnector shall:
          a) be mounted in the distribution board or adjacent to the distribution board in
          the same room,
          b) in the case of the main or first distribution board of an installation, be
          labelled as "main switch",
          c) in the case of a sub-distribution board, be labelled as "sub-main switch" "or
          main switch" if the board is labelled "sub-board…",
          d) in the case where an alternative supply is installed (emergency supply,
          uninterruptible power systems (UPS), etc.), be labelled as required in
          7.12.2.1, and
          e) have a danger notice on or near it. The danger notice shall give instructions
          that the switch-disconnector be switched off in the event of inadvertent
          contact or leakage.

          Comment

          • Dylboy
            Gold Member

            • Jun 2020
            • 777

            #6
            Ahhh yes that is true ! Will use those.

            Also found the below: and as far as I know the installation is the Main DB and not the Kiosk at the wall for the property either.

            6.9.1.1 Each installation shall have one disconnecting device to disconnect
            the entire installation, except in the case of multisupplies or more than one
            transformer supplying the installation where each supply shall have its own
            disconnecting device. There shall be a notice fixed next to each such
            disconnecting device indicating that the installation has more than one main
            switch-disconnector.


            Sent from my CPH2197 using Tapatalk

            Comment

            • Dylboy
              Gold Member

              • Jun 2020
              • 777

              #7
              What are your thoughts on this then.. same House hahaha.

              The little CB is a 15Amo and does the gate motor...

              This is not controlled via main switch in the DB...

              So it's wrong but now to get a feed there from the DB is major major work.

              Sent from my CPH2197 using Tapatalk

              Comment

              • Derlyn
                Platinum Member
                • Mar 2019
                • 1761

                #8
                Originally posted by Dylboy
                What are your thoughts on this then.. same House hahaha.

                The little CB is a 15Amo and does the gate motor...

                This is not controlled via main switch in the DB...

                So it's wrong but now to get a feed there from the DB is major major work.

                Sent from my CPH2197 using Tapatalk
                [ATTACH]8600[/ATTACH]
                Remove the AC supply from gate motor.
                Install a small solar panel to keep the gate battery charged.

                I have done a couple of gate installations that are far from the house.
                40 or 60A/h lead acid battery, solar panel ............ sorted.

                Comment

                • Dylboy
                  Gold Member

                  • Jun 2020
                  • 777

                  #9
                  Ah good idea ! Funny thing is it is not even 10 meters away the DB hahaha.

                  The solar is a good one, a secure complex as well so does not need tobe like farm safe solar haha

                  Sent from my CPH2197 using Tapatalk

                  Comment

                  • Dylboy
                    Gold Member

                    • Jun 2020
                    • 777

                    #10
                    Originally posted by Derlyn
                    Remove the AC supply from gate motor.
                    Install a small solar panel to keep the gate battery charged.

                    I have done a couple of gate installations that are far from the house.
                    40 or 60A/h lead acid battery, solar panel ............ sorted.
                    Uncle, what solar charger do you normally use for this setup if I may ask ?

                    Sent from my CPH2197 using Tapatalk

                    Comment

                    • GCE
                      Platinum Member
                      • Jun 2017
                      • 1483

                      #11
                      Originally posted by Dylboy
                      What are your thoughts on this then.. same House hahaha.

                      The little CB is a 15Amo and does the gate motor...

                      This is not controlled via main switch in the DB...

                      So it's wrong but now to get a feed there from the DB is major major work.

                      Sent from my CPH2197 using Tapatalk
                      [ATTACH]8600[/ATTACH]
                      Assuming the 15 Amp is in the meter box on the boundary next to the mein incoming cable.

                      Install a surface weatherproof DB next to the meter box. Route main cable from house to DB and mains from Meter box - This will be the main DB and the present one will become Sub DB

                      Comment

                      • Derlyn
                        Platinum Member
                        • Mar 2019
                        • 1761

                        #12
                        Originally posted by Dylboy
                        Uncle, what solar charger do you normally use for this setup if I may ask ?

                        Sent from my CPH2197 using Tapatalk
                        South Africa's leading online store. Fast, reliable delivery to your door. Many ways to pay. Shop anything you can imagine: TVs, laptops, cellphones, kitchen appliances, toys, books, beauty & more. Shop the mobile app anytime, anywhere.


                        Chinatown. 20A = R200 ; 30A = R300 ; 40A = R400.

                        Comment

                        • Dylboy
                          Gold Member

                          • Jun 2020
                          • 777

                          #13
                          Originally posted by GCE
                          Assuming the 15 Amp is in the meter box on the boundary next to the mein incoming cable.

                          Install a surface weatherproof DB next to the meter box. Route main cable from house to DB and mains from Meter box - This will be the main DB and the present one will become Sub DB
                          Ah brilliant, I know that trick but didn't even cross my mind sadly. Thank you again GCE !

                          Sent from my CPH2197 using Tapatalk

                          Comment

                          • Dylboy
                            Gold Member

                            • Jun 2020
                            • 777

                            #14
                            Originally posted by Derlyn
                            https://www.takealot.com/20a-solar-c...E&gclsrc=aw.ds

                            Chinatown. 20A = R200 ; 30A = R300 ; 40A = R400.
                            Brilliant ! Perfect price for application and the charge voltages appear to be in line as I read while in a que haha.

                            Nice solution that one !

                            Sent from my CPH2197 using Tapatalk

                            Comment

                            • Isetech
                              Platinum Member

                              • Mar 2022
                              • 2274

                              #15
                              Originally posted by Derlyn
                              https://www.takealot.com/20a-solar-c...E&gclsrc=aw.ds

                              Chinatown. 20A = R200 ; 30A = R300 ; 40A = R400.

                              And as everyone shouts, but they are not approved. You can only smile and shake your head, what is "approved" and if you can buy the product from Chinatown and nobody is regulating then why not.

                              If the house burns down, who cares, the insurance company will come up with some excuse why they are only going to pay out a small percentage or nothing at all.

                              The best part is the "insurance approved contractors", China town has nothing on these contractors. The floods certainly opened the flood gates for every "insurance approved contractors" to come out the wood work