Strange one but i do backup power every now and then, small systems DB tied, but I always struggle with space and it's always on the Neutral bar as with the backup need a seperate N bar. Also most DB Boards the Neutral bars are blocked by the Line cable.
So their is a reg that says all circuits must originate from the same DB.
But thinking a bit can I for example take a small 8way DB and install it next to the main DB and then run my neutrals only to that DB. Or even an enclosure and put a N bus in there only.
Basically I want to make more space for the neutrals that is time efficient.
I cant always install a whole new Sub DB. I just want space for Neutrals haha.
Is it legal as then technically not in the same enclosure as per below ?
I feel it's not but worth a ask I reckon.
6.1.4 All the conductors of any circuit shall originate at the same distribution baord
Sent from my CPH2197 using Tapatalk

Strange one but i do backup power every now and then, small systems DB tied, but I always struggle with space and it's always on the Neutral bar as with the backup need a seperate N bar. Also most DB Boards the Neutral bars are blocked by the Line cable.
So their is a reg that says all circuits must originate from the same DB.
But thinking a bit can I for example take a small 8way DB and install it next to the main DB and then run my neutrals only to that DB. Or even an enclosure and put a N bus in there only.
Basically I want to make more space for the neutrals that is time efficient.
I cant always install a whole new Sub DB. I just want space for Neutrals haha.
Is it legal as then technically not in the same enclosure as per below ?
I feel it's not but worth a ask I reckon.
6.1.4 All the conductors of any circuit shall originate at the same distribution baord
Sent from my CPH2197 using Tapatalk
Comment