Double insulated wire

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Isetech
    Platinum Member

    • Mar 2022
    • 2274

    #1

    Double insulated wire

    A quick question, can you run double insulated wire directly on a wire cable tray AC or DC ?

    why I ask the question is because I see a lot of solar installations with "exposed" (what is suppose to be double insulated) red and black wire.

    Considering the DC from the solar panels are no longer "low voltage", some runs are over 400 VDC.

    This discussion has come up in the past, but regarding "open" wiring.

    The same rules would apply ?
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #2
    I feel yes double insulated you can, as then that is the same as FTE. However not single insulated.

    Sent from my CPH2197 using Tapatalk

    Comment

    • Dylboy
      Gold Member

      • Jun 2020
      • 777

      #3
      Also with solar I am seeing in almost every single one that either AC and DC is in the same trunking or that DC comes through the trunking i.e cuts the AC cable perpendicular....

      Look at every photo shown on social media aswell you will see that their is one trunking at the bottom with battery cables or PV cables in the same trunking...

      Sent from my CPH2197 using Tapatalk

      Comment

      • GCE
        Platinum Member
        • Jun 2017
        • 1483

        #4
        You can run single wire in a wireway
        Obviously not good practice to run single insulated on cable tray

        Dc must be in a separate wireway

        Comment

        • Isetech
          Platinum Member

          • Mar 2022
          • 2274

          #5
          Originally posted by GCE
          You can run single wire in a wireway
          Obviously not good practice to run single insulated on cable tray

          Dc must be in a separate wireway
          If you can run single insulated wire on a cable tray why do some inspectors fail an installation if a short piece of wire is exposed on a downlight? Something to do with the compression on the single insulated wire.

          Installing single insulated wire on a metal cable tray would be a silly thing to do, you would have to make sure the metal cable tray is bonded correctly. Just imagine pulling cable ties tight on a metal tray ... eeeish.

          I see in the UK they only use double insulated open wiring from the meter to the DB.
          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

          Comment

          • Isetech
            Platinum Member

            • Mar 2022
            • 2274

            #6
            Originally posted by Dylboy
            Also with solar I am seeing in almost every single one that either AC and DC is in the same trunking or that DC comes through the trunking i.e cuts the AC cable perpendicular....

            Look at every photo shown on social media aswell you will see that their is one trunking at the bottom with battery cables or PV cables in the same trunking...

            Sent from my CPH2197 using Tapatalk
            It is going to take a few years for the solar industry to settle, its the same as problem we had with generators when load shedding started back in late 2007. That saying "it cant be that bad, everyone doing it".
            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

            Comment

            Working...