Hello 
This may be long winded or not but I have been doing some AC work for a guy who does Victron and then yesterday I took the bottom bracket off the multiplus II 5KVA, 70A. And it said the below pic, I assume the impedance they mean is the External Earth Loop Impedance but that "+j0.18ohm " I do not understand, basically it's the letter j there ?
I assume the 0.28ohm is external earth loop then the +j is the earth loop from inverter to the DB it is fed from... So then a total Zs of 0.46ohm.
Am I correct in the above ?
Then I had a call that the ELU (Earth Leakage Unit) on inverter output intermittently trips when Eskom comes back, there is the internal relay for N and E but the Earth Loop of the Main DB is 0.54ohm so is that why the ELU trips as the Earth loop is too high for it and greater than the combined 0.46ohm?
I can hard wired a N and E but that can not be done past council but since the inverter is an appliance then it can be argued but for now just wanting clarity on the above impedance stuff.

Sent from my CPH2197 using Tapatalk

This may be long winded or not but I have been doing some AC work for a guy who does Victron and then yesterday I took the bottom bracket off the multiplus II 5KVA, 70A. And it said the below pic, I assume the impedance they mean is the External Earth Loop Impedance but that "+j0.18ohm " I do not understand, basically it's the letter j there ?
I assume the 0.28ohm is external earth loop then the +j is the earth loop from inverter to the DB it is fed from... So then a total Zs of 0.46ohm.
Am I correct in the above ?
Then I had a call that the ELU (Earth Leakage Unit) on inverter output intermittently trips when Eskom comes back, there is the internal relay for N and E but the Earth Loop of the Main DB is 0.54ohm so is that why the ELU trips as the Earth loop is too high for it and greater than the combined 0.46ohm?
I can hard wired a N and E but that can not be done past council but since the inverter is an appliance then it can be argued but for now just wanting clarity on the above impedance stuff.

Sent from my CPH2197 using Tapatalk