    Now that we all understand the difference between lightning and surge protection, what are your thoughts on where surge protection should be installed.

    1/ The main DB, at the main switch (non-essential supply) ?

    2/ The Sub DB, at the main switch, after the neutral earth bond (essential supply or inverter output) ?

    3/ The DC combiner box for the panel cables ?

    The reason for the questions, if the building has solar panels and the panels are earthed, bonded and have an earth spike, are class II surge arrestors the correct units?

    Do you need surge protection after the inverter or only in the main DB?
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #2
    My opinion yes because we are doing surge protection and not lightning.

    A direct strike if it was a class 1 or 2 but with no proper lighting protection standards will do nothing.

    When I spoke to DHEN about this he said you can fit a type 1 and Type 2 for extra measure but make sure they are coordinated (basically same brand in a nutshell)

    Earthing of Panels for the sake of earthing can now cause an extra conductor to carry a surge so bonding or earthing a panel in most cases is useless.. unless a metal roof that is already earthing on AC side etc then bonding of panels to roof for same equipotential is then needed.



    Sent from my CPH2197 using Tapatalk

    Comment

    • Dylboy
      Gold Member

      • Jun 2020
      • 777

      #3
      Surge protection in main DB and then Surge protection for PV i.e has + and - as they have better contacts and a lot of stuff I can remember that PV surge is for the PV strings only for when they pick up current that is induced for example near by storm


      I must add I am not qualified in this field but it is what I have learnt and learning.

      Sent from my CPH2197 using Tapatalk

      Comment

      • kavesh
        Bronze Member

        • Feb 2018
        • 168

        #4
        Hi all

        Hope you don't mind me asking a question on this thread. Its related to surge protection.
        I have a 3kva inverter installed.
        I spoke to the electrician and asked what is the best defence against against power surges. Effectively he said that nothing will save you. You can install surge protection in your DB and if the power surge is big it will go past the surge protector and still damage your appliances and inverter.

        I would really appreciate some advice on this. I spent a good some of money installing the invertor and need some sort of protection. Yes there is a fuse fitted but if I recall its more to protect the batteries.

        Thanking you in advance.

        Kavesh

        Comment

        • GCE
          Platinum Member
          • Jun 2017
          • 1495

          #5
          A good quality surge arrestor will protect equipment , if have just seen it again when a neutral was stolen on Friday evening .

          For good quality class1 and 2 combined expect to pay around R1 000 per pole - So +/R2K for a single phase supply

          Comment

          • Isetech
            Platinum Member

            • Mar 2022
            • 2274

            #6
            I agree with the person who mentioned that the lightning/surge protection will not protect you against a direct hit or a really big bang on the council. I can share a few stories about insurance claims going into the 100's of thousands. I also have a few pics of installations where we have installed the best quality surge protection, trip connects and all those nice things, blown to pieces.

            However if you want to spend some money on surge protection to reduce the risk of damage due to transient spikes, heavy load switching during load shedding etc.

            Surge protection in the main DB will help reduce the risk of damaging sensitive electronic equipment, installing surge protection on plug tops for example will also help. Add a trip connect device which will protect against neutral cable theft.

            More important than our advise, check with your insurance, if they require surge protection, best you have it installed.

            From past experience, insurance will cover until the first bang., then they will send you an email with a clause which no longer covers you unless you have surge protection.

            Beware, make sure you read the clauses related to surge protection, most insurances companies will not cover you unless it is lightning related. No storm on the day, no cover. You will have to claim from your local supplier.
            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

            Comment

            • Dylboy
              Gold Member

              • Jun 2020
              • 777

              #7
              Is a trip connect device like those TV safe units ?

              I thought a surge protector will help with a Neutral stolen?

              Sent from my CPH2197 using Tapatalk

              Comment

              • Isetech
                Platinum Member

                • Mar 2022
                • 2274

                #8
                I have a couple 3 phase units on sites where we have low voltage issues, but can be used for over voltages caused by neutral cable theft.

                We still have sites which are FUBAR after "faults on the supply". In some cases the units are melted and welded closed. They do work, because I have had cases where there has been cable theft and the sensitive equipment was not damaged.

                Features: - LCD Display with Green backlight - Multi-Voltage: Three Phase 4 Wire & Three Phase 3 Wire @ 145-500VAC - Protection against: Phase Loss Phase Asymmetry Under & Over Frequency Phase Sequence Under & Over Voltage - Selectable: Under/Over Voltage Phase Loss Under/Over Frequency Asymmetry Phase Sequence - Can be configured for 3 Phase3 Wire / 3 Phase 4 Wire Systems -



                Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                Comment

                • Isetech
                  Platinum Member

                  • Mar 2022
                  • 2274

                  #9
                  If you scratch around on the internet you will find a product that looks identical to the trip connect. I dont know if the clearline product is rebranded.
                  Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                  Comment

                  • Dylboy
                    Gold Member

                    • Jun 2020
                    • 777

                    #10
                    Ahhh yes ok, you have mentioned it before sorry, I didn't quite click. But also good reminder of the product!

                    Very cool stuff that thank you.

                    Sent from my CPH2197 using Tapatalk

                    Comment

                    • Derlyn
                      Platinum Member
                      • Mar 2019
                      • 1765

                      #11
                      As far as load shedding is concerned, I'm still convinced that my fridge safe together with contactor is the answer.

                      My power comes on a couple of minutes after everyone else's and I'm sure the spikes caused by switching on are long gone by the time mine comes on.

                      I have noticed that led lights are prone to failure because of spikes from loadshedding. How do I know this you may ask.? I have had many clients complaining that led lamps were blowing left right and centre. I suggested that when there's loadshedding to switch off the lights and only to switch them on again after the power has been turned back on. End of problem.

                      Comment

                      • Isetech
                        Platinum Member

                        • Mar 2022
                        • 2274

                        #12
                        The spikes are recorded as load shedding is switched, on both, on and off. The bottom line is load shedding is doing a lot more damage than we identify. Its good busy for maintenance sparkies. A drive in a machine could cost in excess of R100 000 .

                        Rather focus on your insurance, make sure you understand your cover and check that there is no clause which voids surges caused by anything other than lightning. The assessor will check the weather report for the day of the claim. Dont say you weren't warned, I see the insurance companies handing out proper wedgies to loyal customers who pay and think they are covered.

                        Insurance companies are about collecting monthly revenue not paying out share holder profits.


                        Originally posted by Derlyn
                        As far as load shedding is concerned, I'm still convinced that my fridge safe together with contactor is the answer.

                        My power comes on a couple of minutes after everyone else's and I'm sure the spikes caused by switching on are long gone by the time mine comes on.

                        I have noticed that led lights are prone to failure because of spikes from loadshedding. How do I know this you may ask.? I have had many clients complaining that led lamps were blowing left right and centre. I suggested that when there's loadshedding to switch off the lights and only to switch them on again after the power has been turned back on. End of problem.
                        Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                        Comment

                        • Isetech
                          Platinum Member

                          • Mar 2022
                          • 2274

                          #13
                          The moral of the story, just like you pay the school teacher, teller at the bank and "insurance broker a monthly fee, make sure you get them to go through your policy step by step even if it means they must do a site visit and 5 hours to verify everything in the document and highlight everything you are not sure about. When that wall collapses or the drive pops, they will refer to the document you signed, its all there in the document.
                          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                          Comment

                          • kavesh
                            Bronze Member

                            • Feb 2018
                            • 168

                            #14
                            Thanks for the comments guys, lots of food for thought.

                            My current policy only covers R10k which is nothing sadly. I was asking my broker to increase the cover and she mentioned that the insurance companies are loading premiums for higher cover, which can make it challenging for the lay man to accept.
                            I was also told that the insurance companies are insisting on surge protection, but as far as I have read my policy does not stipulate this, but will confirm with the broker again.

                            Seems we are getting screwed all round....

                            Comment

                            • Derlyn
                              Platinum Member
                              • Mar 2019
                              • 1765

                              #15
                              Fortunately, I've never had insurance.

                              Not once have I paid for other people's stuff to be replaced.

                              Comment

                              Working...