Separating the DC in a solar system.

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Isetech
    Platinum Member

    • Mar 2022
    • 2274

    #1

    Separating the DC in a solar system.

    We all know that you cannot run AC and DC and comms cables together, what about battery cables and solar panel cables?

    You battery cables are generally between 12 VDC and 48 VDC and in older solar systems the voltage was around 120 VDC.

    Things have changed, the question is can you fit a DC Distribution board and use it to house all the DC safety gear and fuses?

    Can I fit one DB, fit the fuse protection for the batteries and the solar panel fuses in the same DB?

    Can I run the all the DC cables in the same wireway, if the batteries are 48 VDC and the solar panels are 450 VDC?
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.
  • GCE
    Platinum Member
    • Jun 2017
    • 1483

    #2
    Generally you will not run battery and PV together
    Battery will need a fuse in a holder because of the bidirectional current and DC C/Breakers cant all handle bi directional current
    Pv you need to go into an isolator , fuse and onto DC surge arrestors per string
    Surge arrestor is DC and designed for PV panels

    If you do have them in the same trunking the cables would need to be able to handle the highest voltage

    Comment

    • Dylboy
      Gold Member

      • Jun 2020
      • 777

      #3
      So can PV cables be in same trunking, conduit, wireways as AC cables ?

      I see it on almost every single solar installation

      Sent from my CPH2197 using Tapatalk

      Comment

      • Dylboy
        Gold Member

        • Jun 2020
        • 777

        #4
        Valsa supplier have a AC and DC protection box... Double tier with both the AC protection and the DC protection... Is that allowed ? They bark on about being SANS what what but then I see this.

        Also seen them use an AC isolator for DC, I asked the sales guy and he just said well they had engineers design and build it....

        Sent from my CPH2197 using Tapatalk

        Comment

        • Isetech
          Platinum Member

          • Mar 2022
          • 2274

          #5
          Originally posted by GCE
          Generally you will not run battery and PV together
          Battery will need a fuse in a holder because of the bidirectional current and DC C/Breakers cant all handle bi directional current
          Pv you need to go into an isolator , fuse and onto DC surge arrestors per string
          Surge arrestor is DC and designed for PV panels

          If you do have them in the same trunking the cables would need to be able to handle the highest voltage
          Everyone connecting batteries and solar panels, take note of these comments. If you have double insulated solar DC cables which should be rated to 600 or 1000 VDC, makes sure your battery cables are also rated to the string total open VOC.
          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

          Comment

          • GCE
            Platinum Member
            • Jun 2017
            • 1483

            #6
            Originally posted by Dylboy
            So can PV cables be in same trunking, conduit, wireways as AC cables ?

            I see it on almost every single solar installation

            Sent from my CPH2197 using Tapatalk
            No they may not - Unfortunately certain PV installers keep saying there are no regulations governing PV - They seem to miss the point that PV is Electrical installation work as defined and falls directly under SANS10142-1
            Clause 6.1.10 is clear

            6.1.10 Conductors that form part of a d.c. installation shall not be run in the
            same wireway as conductors that form part of an a.c. installation.

            Comment

            • GCE
              Platinum Member
              • Jun 2017
              • 1483

              #7
              Originally posted by GCE
              Generally you will not run battery and PV together
              Battery will need a fuse in a holder because of the bidirectional current and DC C/Breakers cant all handle bi directional current
              Pv you need to go into an isolator , fuse and onto DC surge arrestors per string
              Surge arrestor is DC and designed for PV panels

              If you do have them in the same trunking the cables would need to be able to handle the highest voltage
              6.1.7 If conductors that operate at different voltages run in the same wireway,
              the insulation of each conductor shall be able to withstand the highest
              conductor voltage in the wireway. Alternatively, the conductors shall be
              separated by a continuous barrier of insulating material or earthed metal.


              6.3.2.2 Conductors shall be so insulated as to withstand the highest
              temperature and voltage to which they are likely to be exposed.

              Comment

              • Isetech
                Platinum Member

                • Mar 2022
                • 2274

                #8
                I dont see a problem with using sprag to sleeve the wire to protect the cable /wire, it just cant touch at any point, even at a 90 degree cross.

                The 90 degree crossing of cables/wires has nothing to do with voltages.

                Networks, frequencies and stuff is a completely different topic, in some cases if a VSD is used you would also need to consider cable routes and cross over, shielded cables, etc.
                Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                Comment

                • Dylboy
                  Gold Member

                  • Jun 2020
                  • 777

                  #9
                  Originally posted by GCE
                  No they may not - Unfortunately certain PV installers keep saying there are no regulations governing PV - They seem to miss the point that PV is Electrical installation work as defined and falls directly under SANS10142-1
                  Clause 6.1.10 is clear

                  6.1.10 Conductors that form part of a d.c. installation shall not be run in the
                  same wireway as conductors that form part of an a.c. installation.
                  I agree, DC and AC always seperate.

                  I do see with these inverters and the layout of the install or nature where it is they have cross over.

                  Can DC cut through AC wireway ?
                  I say no as it is in the same wireway but I want to make sure.

                  I think I have seen one install where AC and DC was seperate everywhere

                  Sent from my CPH2197 using Tapatalk

                  Comment

                  • Isetech
                    Platinum Member

                    • Mar 2022
                    • 2274

                    #10
                    Originally posted by Dylboy
                    I agree, DC and AC always seperate.

                    I do see with these inverters and the layout of the install or nature where it is they have cross over.

                    Can DC cut through AC wireway ?
                    I say no as it is in the same wireway but I want to make sure.

                    I think I have seen one install where AC and DC was seperate everywhere

                    Sent from my CPH2197 using Tapatalk
                    My understanding is, so long as you protect the cables from each other. You cant just cut a hole in the trucking and have all the cables touching each other.

                    The reality is you never every stop it from happening.
                    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                    Comment

                    Working...