    Trunking, Network and power cables?

    I've been informed that Network cables and power cables cannot occupy the same physical space (one single run of trunking)

    The network cable I intend to use is unshielded Cat5E, or possibly shielded Cat6.

    Q1. Does that requirement apply to Shielded earthed surfex cable?
    Q2. Is it okay to have 2 trunkings side by side, one carrying shielded earthed surfex power, the other carrying network?
    Q3. Is it okay for Network cable to be inside trunking, and surfex cable to be outside the trunking, attached directly to the wall (nail clips), where the outside of the surfex cable is touching the trunking? (meaning right next to it)
  • GCE
    Platinum Member
    • Jun 2017
    • 1483

    #2
    The 2 regs pasted from SANS 10142-1 below, should answer all of the above questions

    6.1.7 If conductors that operate at different voltages run in the same wireway,
    the insulation of each conductor shall be able to withstand the highest
    conductor voltage in the wireway. Alternatively, the conductors shall be
    separated by a continuous barrier of insulating material or earthed metal.


    6.3.2.2 Conductors shall be so insulated as to withstand the highest
    temperature and voltage to which they are likely to be exposed.

    Comment

    • LightsOn
      Full Member
      • Sep 2022
      • 33

      #3
      Thanks @GCE. I would love to take your answer and run with it, but to be sure, is there perhaps not some other regulation with regard to not mixing power and data in the same wireway/trunk, that causes some other regulation to apply other than SANS 10142-1 6.1.7 and 6.3.2.2 ?
      Or perhaps categorization of user-operated wiring (network cables with RJ45 jacks exposing conductors) vs electrical?

      Obviously from a technical perspective, there is plenty of redundant layers of insulation between the wiring, each in their own capacity able to provide the necessary insulation. So it's perfectly safe.
      I'm just asking from a legal standards perspective.

      Comment

      • Isetech
        Platinum Member

        • Mar 2022
        • 2274

        #4
        Running 2 pieces of trunking side by side shouldn't be a problem, if you use surfix and a shielded cat 5 or 6 cable. You just need to make sure you dont get interference on the network cable.

        I was taught that you dont earth both sides of the shield on a network cable, only one side.

        In some cases people use PVC sprag as a barrier in the same trunking.
        Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

        Comment

        • LightsOn
          Full Member
          • Sep 2022
          • 33

          #5
          Thanks @Isetech.
          I'd be very happy if I can just put the Surfix and network cable in the same trunk. That would be first prize

          Originally posted by Isetech
          I was taught that you dont earth both sides of the shield on a network cable, only one side.
          I've also read that.

          However, as a random unrelated side-note.

          I once ran an inverter via a 25 meter extension cable to a multi-plug, then powered a PC from it, etc. The problem is when you touched the keyboard you'd get a mild (but too unpleasant to keep touching) shock. I'm not sure if that extension cable had a problem with it's grounding pin. But anyway, I solved the problem by taking 2x 3pin plugs and just wiring only a single green ground wire, and plugging one end into the wall, the other into the multi-plug. And that put an end to the shocking experience.

          Comment

          • LightsOn
            Full Member
            • Sep 2022
            • 33

            #6
            I found this thread where they seem to be relatively certain that DC and AC wire and also inverter AC vs Eskom AC must all be in separate trunking.
            https://powerforum.co.za/topic/8085-...le-wiring-coc/

            I was reading in DRAFT: SANS 10142-1-2:20XX
            And all that I could find related to this was
            Section 8.1 - 26. The DC circuits are electrically separated from the AC circuits

            But that says "electriaclly separated".
            Note that it doesn't say "physically" or "mechanically" separated. Electrically just means that there's no conductance. Having an insulated AC wire touching a network cable on the outside IS electrically separated.

            It's so annoying how there are so many different regulations and different people focus on different sets of regulations and also interpret them differently.

            It's such a simple question, there should be a simple definitive answer.

            Comment

            • LightsOn
              Full Member
              • Sep 2022
              • 33

              #7
              Originally posted by GCE
              [I]6.1.7 If conductors that operate at different voltages run in the same wireway,
              the insulation of each conductor shall be able to withstand the highest
              conductor voltage in the wireway. Alternatively, the conductors shall be
              separated by a continuous barrier of insulating material or earthed metal.
              What about 6.1.10, though...
              Originally posted by SANS10142-1
              6.1.10 Conductors that form part of a d.c. installation shall not be run in the
              same wireway as conductors that form part of an a.c. installation.
              Are network cables considered to be "part of a DC installation" ?

              I'm wondering if "DC installation" only refers to DC power cables (eg: PV or battery power cables) or if it includes to data cables as well.
              Last edited by LightsOn; 24-Sep-22, 11:25 AM.

              Comment

              • LightsOn
                Full Member
                • Sep 2022
                • 33

                #8
                Oh, I see SANS 10142-1 2017 ed2 says:
                7.15 D.C. installations
                "NOTE such as telecommunication installations and the like."

                Well that settles that, then.

                So definitively, power and network cables cannot run in the same trunking.

                @GCE, let me know if you're unsure about anything else, maybe I can help you.

                Comment

                • Isetech
                  Platinum Member

                  • Mar 2022
                  • 2274

                  #9
                  GCE shares a lot of useful content on this forum and the content is a clear indication that he has been around the block a few times like many of us.



                  Originally posted by LightsOn
                  Oh, I see SANS 10142-1 2017 ed2 says:
                  7.15 D.C. installations
                  "NOTE such as telecommunication installations and the like."

                  Well that settles that, then.

                  So definitively, power and network cables cannot run in the same trunking.

                  @GCE, let me know if you're unsure about anything else, maybe I can help you.
                  Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                  Comment

                  • Isetech
                    Platinum Member

                    • Mar 2022
                    • 2274

                    #10
                    SANS 10142-1 - 2021 (ed 3.01) is the latest addition to the regs.
                    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                    Comment

                    • LightsOn
                      Full Member
                      • Sep 2022
                      • 33

                      #11
                      Originally posted by Isetech
                      GCE shares a lot of useful content on this forum and the content is a clear indication that he has been around the block a few times like many of us.
                      Yes, it was apparent to me that GCE is highly experienced and knowledgeable from his posts. No surprises for me there.

                      I believe it's best to have an open, beginner's mind and that we all have something to learn; whether we want to or not. So it's been very interesting on the forum here.

                      Originally posted by Isetech
                      SANS 10142-1 - 2021 (ed 3.01) is the latest addition to the regs.
                      Thank you!