So was sitting in traffic as one does in laodshedding and had a thought...
The neutral conductor shall at least be the same CSA as the phase conductor.
Now the above is great for single phase but then with 3 phase we now have 3 current carrying conductors.
So let's say all wired in 16mm cable the phases and Neutral. On a 60Amp triple pole CB.
But if each phase had to pull 50Amps that neutral won't be able to carry 150Amps !
So is this just due to domestic homes and diversity being used or am I missing something ?
I get it there where 3 single phase machine always running at 50Amps then the Neutral is sized accordingly i.e for 150Amps (well more but for sake of conversation and maths let's stick with easy numbers)