V0V Generator

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Andrew_van_Zyl
    Bronze Member

    • Mar 2022
    • 131

    #1

    V0V Generator

    Sorry to bring this up again but can anyone point me in the right direction?

    I tested 140V L-E, and 80V N-E.

    Adendorff assure me that if I bond neutral and earth I will get 220V V00. I've popped two Automatic Voltage Regulators since attempting this. Adendorff are unable to tell me why this is happening.

    My City Power arrangement is 3 phase, neutral and earth are bonded and then separated in the DB.

    I use a 3 phase changeover switch with live from the gen supplying all 3 phases.

    Please excuse my crude drawing of the installationClick image for larger version

Name:	Generator.jpg
Views:	1
Size:	31.0 KB
ID:	270006

    Any suggestions how I can make this safe (apart from setting fire to the thing)?
  • Derlyn
    Platinum Member
    • Mar 2019
    • 1765

    #2
    One question. Did you get those readings with no load or was that with a load connected ?

    When checking generator voltages, always do it with a load connected. A 40W incandescent lamp as load will work.

    If your readings stay the same with a small load connected, then it's a VOV wound alternator and the neutral and earth cannot be connected together without first removing the centre tap earth connection on the stator.

    If you bridge neutral and earth on a VOV wound alternator, you are basically shorting out half the windings on the stator and somethings gonna pop.

    Comment

    • GCE
      Platinum Member
      • Jun 2017
      • 1495

      #3
      SANS requires a 4 pole change over
      You could be creating problems with your neutral still linked to mains and earthing the incoming neutral
      You may have become a better earth star point for the street

      Comment

      • Andrew_van_Zyl
        Bronze Member

        • Mar 2022
        • 131

        #4
        Light bulb moment... of course! This forum has been so incredibly generous with their time and knowledge - thank you.

        As I see it I have 2 issues - a N & E bonding issue, and potentially a V0V issue (to be tested as per Derlyn)

        I plan to replace the current 3-pole with a 4-pole changeover, and change the earthing arrangements to isolate the 2 supply systems to work independently as below:

        Click image for larger version

Name:	Generator-Page-2.jpg
Views:	1
Size:	30.7 KB
ID:	266227

        All good?

        Comment

        • Isetech
          Platinum Member

          • Mar 2022
          • 2274

          #5
          The bond must be on the generator, not the grid power.
          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

          Comment

          • Derlyn
            Platinum Member
            • Mar 2019
            • 1765

            #6
            Both the grid and the alternator must each have their own bonds .

            ie. When installation connected to grid, the bond is on the grid.
            When installation connected to alternator, the bond is on the alternator.
            Last edited by Derlyn; 13-Dec-22, 07:50 AM.

            Comment