This is an interesting topic, looking at some of the installations.
How do you decide what size cable and fuse protection to install.
The first thing you need to look at, the battery rating. A 100 amp hr (5 kwh) battery with a 0.5 C rating would mean that the fuse protection should be around 70 amp and the cable would need to be at least 16mm. I have noticed some 25 mm silicon multi cord flexible cable is rated at over 200 amps, why would you need a 200 amp cable for a 0.5 C rated battery.
Lets say you decided to install 2 batteries, then a 125 amp fuse would be a wise choice using 25 or 35 mm cable.
Its not always that simple, the lithium batteries have special terminals, which have a 25mm lugs.
I have an installation where we will be installing a 8 kva unit with 4 x 5 kwh batteries, that job is going to get interesting. Selecting the fuse and cable layout is going to be interesting. You have the choice of parallel or cascade parallel connections.
How do you decide what size cable and fuse protection to install.
The first thing you need to look at, the battery rating. A 100 amp hr (5 kwh) battery with a 0.5 C rating would mean that the fuse protection should be around 70 amp and the cable would need to be at least 16mm. I have noticed some 25 mm silicon multi cord flexible cable is rated at over 200 amps, why would you need a 200 amp cable for a 0.5 C rated battery.
Lets say you decided to install 2 batteries, then a 125 amp fuse would be a wise choice using 25 or 35 mm cable.
Its not always that simple, the lithium batteries have special terminals, which have a 25mm lugs.
I have an installation where we will be installing a 8 kva unit with 4 x 5 kwh batteries, that job is going to get interesting. Selecting the fuse and cable layout is going to be interesting. You have the choice of parallel or cascade parallel connections.