LED indicator lights for DB and panels

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Isetech
    Platinum Member

    • Mar 2022
    • 2274

    #1

    LED indicator lights for DB and panels

    This has become an interesting topic

    I use a din rail mount LED for grid and UPS and install a 1 amp fuse inline, just in case.

    What is the big deal, fault levels and the ability for the wire to carry that fault if one occurs.

    I have builtmany many panels in my time which included panel indicator lights, in most cases they were part of a control circuit protected by a control circuit breaker of fuses.

    What size wire do you use to connect the LED indicator light to the circuit breaker, do you install a circuit breaker or fuse to protect the wire for the indicator light.

    I also work in places where there are 3000 amp circuits with thin wires feeding off the main bussbar to a meter, protected by a fuse.

    What are your thoughts on fault levels, thin wires and indicator lights being used in backup systems?
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #2
    I use the inline fuse for the indicator lights as not always space for a circuit breaker.

    Sent from my CPH2197 using Tapatalk

    Comment

    • Justloadit
      Diamond Member

      • Nov 2010
      • 3518

      #3
      I would think, it depends on where the fuse is placed.
      If the fuse is placed close to the source, then the fuse will protect the wire to the indicator lamp, in the case the wire gets compromised mechanically after the fuse.
      If the fuse is close to the indicator lamp, then it may only protect the wire from the fuse to the lamp if it fails in a short circuit mode.
      Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
      Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

      Comment

      • GCE
        Platinum Member

        • Jun 2017
        • 1473

        #4
        We generally use a CB in the small DB's under 100Amp

        In the bigger DB's you need to get the fuse holder that munts onto the busbar and can handle the fault level otherwise your wire size has to match fault levels - On a 10KA fault level DB your wire size needs to be at least 16sqmm

        Rule of thumb is 1sqmm per 1 KA of fault level
        Actually thought it was a note in the regulations but I don't find it



        6.6.1.13 In a distribution board where the short-circuit rating exceeds 10 kA,
        the mechanical strength of the conductors installed between the busbars and
        the functional units shall be sufficient to withstand the short- circuit stresses
        which could occur. A conductor with a minimum cross-sectional area of
        16 mm2 shall be used if it cannot be shown by calculation or from the
        component manufacturer's information that a smaller conductor can be
        installed
        Last edited by Dave A; 01-May-23, 09:48 AM. Reason: made important correction per next three posts' discussion

        Comment

        • Isetech
          Platinum Member

          • Mar 2022
          • 2274

          #5
          It our part of the world the max fault level for domestic installation is genrally 2.5 ka, hence the use of 2.5 or 3 ka mcb's

          The reason for the fuse and not an mcb is because of the limited space.

          The fuse is used between the main switch and the led indicator light. The fault level measured is normally between 260 and 450 amps, so a 0.5 mm wire would be fine and considering ti is in a fault free zones and the chance of it being damaged is literally zero.

          I think you got the 1 KA fault level needs to be 16 sq mm and 1 sqmm rule of thumb mixed up ?

          Originally posted by GCE
          We generally use a CB in the small DB's under 100Amp

          In the bigger DB's you need to get the fuse holder that munts onto the busbar and can handle the fault level otherwise your wire size has to match fault levels - On a 1KA fault level DB your wire size needs to be at least 16sqmm

          Rule of thumb is 1sqmm per 1 KA of fault level
          Actually thought it was a note in the regulations but I don't find it



          6.6.1.13 In a distribution board where the short-circuit rating exceeds 10 kA,
          the mechanical strength of the conductors installed between the busbars and
          the functional units shall be sufficient to withstand the short- circuit stresses
          which could occur. A conductor with a minimum cross-sectional area of
          16 mm2 shall be used if it cannot be shown by calculation or from the
          component manufacturer's information that a smaller conductor can be
          installed
          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

          Comment

          • Isetech
            Platinum Member

            • Mar 2022
            • 2274

            #6
            This is the LEd, I had my first fail on one of these. I see they yave a PCB in side with an LED. I should check with Onesto to see if there is any built in protection.

            https://www.onesto.cn/product/KCI-1L-1007.html


            Maybe a terminal fuse might be a better option, then I can use a 2.5 mm from the double pole isolator to the terminal and a 1.5 mm from the fuse to the LED lamp.
            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

            Comment

            • GCE
              Platinum Member

              • Jun 2017
              • 1473

              #7
              Originally posted by GCE
              We generally use a CB in the small DB's under 100Amp

              In the bigger DB's you need to get the fuse holder that munts onto the busbar and can handle the fault level otherwise your wire size has to match fault levels - On a 10KA fault level DB your wire size needs to be at least 16sqmm

              Rule of thumb is 1sqmm per 1 KA of fault level
              Actually thought it was a note in the regulations but I don't find it



              6.6.1.13 In a distribution board where the short-circuit rating exceeds 10 kA,
              the mechanical strength of the conductors installed between the busbars and
              the functional units shall be sufficient to withstand the short- circuit stresses
              which could occur. A conductor with a minimum cross-sectional area of
              16 mm2 shall be used if it cannot be shown by calculation or from the
              component manufacturer's information that a smaller conductor can be
              installed
              Thanks Isetech
              Yes I left the "0" - should have matched the regulation 10Ka Db needs 16sqmm wire size

              Comment

              • Isetech
                Platinum Member

                • Mar 2022
                • 2274

                #8
                This is what I am trying to understand, how we have 2.5 mm house (prewired at the panels building) inside an 800 amp DB for metering.

                Thats why I thought, its just an LED lamp with a bit of electronics to idicate the power is on or off, just like in the LED retrofits, (we had this discussion a while back) I thought a fuse would save the day.

                My thought are to make a short bussbar with a fuse attached dirrectly to the fuse holder. I need to make the part that fits into the breaker bigger so so a 4 mm wire flattened and soldered onto the fuse holder will make agood contact in the breaker and offer the fault level protection.
                Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.