    Generator earthing

    When I connect a fixed generator using a 4 pole change over switch to a large DB. Can I connect the earth of the generator to the common earth busbar in the panel?
  • GCE
    Platinum Member

    • Jun 2017
    • 1473

    #2
    Originally posted by Jurie999
    When I connect a fixed generator using a 4 pole change over switch to a large DB. Can I connect the earth of the generator to the common earth busbar in the panel?
    You must earth on the common earth bar as per clause 7.12.3.1.1


    SANS 10142-1
    7.12.3.1.1 Protection in accordance with the requirements of 6.7 shall be
    provided for the electrical installation in such a manner as to ensure correct
    operation of the protection devices, irrespective of the source of supply or
    combination of sources of supply. Operation of the protection devices shall
    not rely upon the connection to the earthed point of the main supply when the
    generator is operated as a switched alternative to the main supply.
    Where there is no existing earth electrode installed in the electrical installation,
    a suitable earth electrode may be installed in accordance with SANS 10199.
    When installed, the electrode shall be bonded to the consumer's earth terminal
    and to the earthing point on the alternate supply b
    y a conductor of at least half
    the cross-section of that of the phase conductor, but not less than 6 mm2
    copper, or equivalent. This also applies to a single-phase supply
    (see also 5.2.3.1).