When you install more than one battery with one or more inverters, how many DC disconnects or isolators should be installed.
Taking into consideration that there is more than one method of connecting batteries, series parallel, cascade parallel, there seems to be a little confusion.
If you have one battery and one inverter, simple 100 amp/hr battery, 160 amp fuse disconnect and 125 amp fuse and everyone is happy.
Now you put 2 batteries and 1 inverter, things start getting a little more confusing.
Now look at a rack of batteries and all logic just seems to go out the window, it's not that bad.
If you connect 2 batteries in parallel then you need to consider a few things, the C rating of the battery, which is very important.
A C0.5 100 amp/hr battery connected in parallel, shouldn't charge/discharge each above 50 amp if you want the battery to last a long time.
A C1 100 amp/hr battery on the other hand could charge/discharge at 100 amp each.
IF you are designing a sytem, do you take the C rating into consideration or do you take the inverter max charge discharge rate into consideration.
I suppose it depends on the customer budget. If you install an inverter with a 200 amp max charge/discharge, then you should install 2 x C1 rated 100 amp hr batteries. So a 250 amp fuse disconnect is reuired using at least 50 sqmm battery cable suitable for the voltage rating. If you use a busbar, it must be rated at least 200 amps.
Taking into consideration that there is more than one method of connecting batteries, series parallel, cascade parallel, there seems to be a little confusion.
If you have one battery and one inverter, simple 100 amp/hr battery, 160 amp fuse disconnect and 125 amp fuse and everyone is happy.
Now you put 2 batteries and 1 inverter, things start getting a little more confusing.
Now look at a rack of batteries and all logic just seems to go out the window, it's not that bad.
If you connect 2 batteries in parallel then you need to consider a few things, the C rating of the battery, which is very important.
A C0.5 100 amp/hr battery connected in parallel, shouldn't charge/discharge each above 50 amp if you want the battery to last a long time.
A C1 100 amp/hr battery on the other hand could charge/discharge at 100 amp each.
IF you are designing a sytem, do you take the C rating into consideration or do you take the inverter max charge discharge rate into consideration.
I suppose it depends on the customer budget. If you install an inverter with a 200 amp max charge/discharge, then you should install 2 x C1 rated 100 amp hr batteries. So a 250 amp fuse disconnect is reuired using at least 50 sqmm battery cable suitable for the voltage rating. If you use a busbar, it must be rated at least 200 amps.

Comment