Inverter/transformer neutral earth connection.

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Gtfast
    Full Member

    • Apr 2016
    • 78

    #1

    Inverter/transformer neutral earth connection.

    Hi all
    A friend has a Yamaha generator .
    Internally it has no neutral to earth connection.
    The Earth leakage will not trip when tested with EL tester .
    There is also a polarity fault because one side of the winding is not connected to earth.
    Where is the Protection.
    One cannot connect neutral to earth externally.
    He also has an inverter with the same setup.
    What is the solution.
    Some discussion would be appreciated.
    Thank you




    Sent from my CPH2197 using Tapatalk
  • Derlyn
    Platinum Member

    • Mar 2019
    • 1748

    #2
    First thing to do is take some voltage readings with a load connected to the generator. L-N ?
    L-E ? N-E ?

    Report back..

    Comment

    • Thys LOW Elektries
      Silver Member

      • Jan 2021
      • 269

      #3
      Once the L-N, L-E, and N-E readings have been taken, a missing Star point will most probably be diagnosed.
      Cheap over-the-counter generators and those bought at Makro and Game very seldom if ever a Star point or like they say "Neutral to Earth bond"
      A star point will have to be created if there is none. Various discussions had been done on which way is best so I'm not going to comment on that issue.

      Comment

      • Thys LOW Elektries
        Silver Member

        • Jan 2021
        • 269

        #4
        https://www.theforumsa.co.za/forums/...backup-systems go read that if you have time Very informative

        Comment

        • Gtfast
          Full Member

          • Apr 2016
          • 78

          #5
          Hi Thanks

          That's the confusing thing.
          I would consider it not a cheap Generator.

          I am still waiting on voltages.

          Why is no neutral earth bond provided.
          The generator is like a safety supply????
          Are we just not buying the correct Generators for house supply.

          I will read further.

          Thanks


          Sent from my CPH2197 using Tapatalk

          Comment

          • GCE
            Platinum Member

            • Jun 2017
            • 1473

            #6
            Originally posted by Gtfast
            Hi Thanks


            Why is no neutral earth bond provided.
            The generator is like a safety supply????
            Are we just not buying the correct Generators for house supply.
            Yip - incorrect gensets being used from design and then generally also sizing , but in typical South African fashion we make a plan to make it work

            SANS 10142-1
            7.12.2.7 A 230 V generator with a V-O-V earth connection (centre tap on
            winding which is earthed), shall not be connected to a fixed electrical
            installation.
            NOTE Such a generator may be used as a free-standing unit to provide power to
            specific appliances.

            Comment

            • Gtfast
              Full Member

              • Apr 2016
              • 78

              #7
              Here are the voltages of the generator.

              No load
              L TO N. 232V
              E TO N 3v
              E TO L. 3V

              With 300w load.
              E TO N 11v
              E TO L. 11v

              Not sure about fault current if connecting neutral to earth.Will the generator not get damaged.

              Sent from my CPH2197 using Tapatalk

              Comment

              • Derlyn
                Platinum Member

                • Mar 2019
                • 1748

                #8
                Ok. This generator is not vov wound.
                Hopefully it is connected properly through a change over switch. If so, the earth and neutral can be bridged on the generator. I have done this many times with success.

                Comment

                • Derlyn
                  Platinum Member

                  • Mar 2019
                  • 1748

                  #9
                  Bridging the neutral and earth will only damage the generator if it is vov wound, which this one according to the voltages is clearly not.

                  Comment

                  • Isetech
                    Platinum Member

                    • Mar 2022
                    • 2274

                    #10
                    I removed ad blocker, because Youtube no longer allow registration, it has made this site a terrible experience
                    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                    Comment

                    • Gtfast
                      Full Member

                      • Apr 2016
                      • 78

                      #11
                      Hi
                      What about prospective short circuit current.(fault current).Will this not damage the generator.
                      Is there something I am not understanding.

                      Sent from my CPH2197 using Tapatalk

                      Comment

                      • Derlyn
                        Platinum Member

                        • Mar 2019
                        • 1748

                        #12
                        The generator has circuit breaker on it's output for overcurrent protection.

                        Comment

                        • Gtfast
                          Full Member

                          • Apr 2016
                          • 78

                          #13
                          Thank you.


                          Sent from my CPH2197 using Tapatalk