    Generator 2x socket outputs

    Hello : )

    So client wants Genny installed.

    It has 2x socket outlets.
    7KVA Genny, Grip brand.

    Now I assume the socket outlet is rated at 16Amps.

    So can I combine each socket line and neutral to one so that we don't overload the one socket outlet?

    So basically 2x plug tops from the Genny output and then join the line and neutral to a 4mm˛ cable to the changeover.

    Any advice would be appreciated. : )

    Sent from my CPH2197 using Tapatalk
  • GCE
    Platinum Member

    • Jun 2017
    • 1473

    #2
    Is there not a CB that feeds the 2 sockets
    I would open up behind the sockets and find the main wires coming from the alternator and maybe fit a 32 Amp welding socket

    I have seen people join the 2 x 16amp plug top circuits together to a 4sqmm wire into the house and it gives me the creeps - If 1 plug top is left out then the pins are live

    Comment

    • Isetech
      Platinum Member

      • Mar 2022
      • 2274

      #3
      I use a 4mmx 3 core trailing cable, connected directly into the box on ther generator with a compression gland and a 32 amp 3 pin female connector long enough to reach the 3 pin plug top mounted on the wall.

      I normally install an IP 65 DB under the meter, where I connect the earth spike and fit the changeover switch and circuit breakers etc rteuired to make the installtion as reasonabley safe as possible. Will send you some pics.
      Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

      Comment

      • Dylboy
        Gold Member

        • Jun 2020
        • 777

        #4
        Thanks all! Didn't even think of what would happen if one was left out of the double socket, will try wire direct from the back to a 32Amp. Safer for sure

        Sent from my CPH2197 using Tapatalk

        Comment

        • Isetech
          Platinum Member

          • Mar 2022
          • 2274

          #5
          The person who came up[ with this idea must be the same person who shared the idea of installing DC control boxes with 2 serprate double pole DC isolators connected to the same MPPT and not using MC4 connecotrs on the so called home made "combiner box" Some might say but there are MC4 connectors at the panels, just smile.

          Originally posted by GCE
          Is there not a CB that feeds the 2 sockets
          - If 1 plug top is left out then the pins are live
          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

          Comment

          • Derlyn
            Platinum Member

            • Mar 2019
            • 1748

            #6
            As a matter of interest, how many circuit breakers are an the genny output and what is/are their rating ?

            Comment

            • BEVIN
              Full Member
              • Aug 2018
              • 35

              #7
              Hi oh wise ones please enlighten me. Icw generators that old problem of the three lights on the plug tester(I think no earth?) is it adressed by what method. Please help
              Thanks

              Comment

              • Dylboy
                Gold Member

                • Jun 2020
                • 777

                #8
                On my plug tester 3 lights is good.

                So I am not 100% what may be going on.



                Sent from my CPH2197 using Tapatalk

                Comment

                • Dylboy
                  Gold Member

                  • Jun 2020
                  • 777

                  #9
                  What you may need to do is to disconnect the Genny output Earth, and then link the cable to the installation neutral and earth (create a TNCS) and then also drop an Earth spike or 10 depending on readings.



                  Sent from my CPH2197 using Tapatalk