    Metal conduit as earth

    Have a disagreement with a "master electrician". They beat our quote on rewiring some old flats. Metal conduit with VIR. They rewired but haven't put a earth cable in with the new light circuits. He says yes, I say as it's a rewire a wireway (old metal conduit) shall not be used as earth. Client is a little angry. Tell me I'm not going mad.
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #2
    6.12.1.3 A wireway shall not be used as an earth continuity conductor

    Sent from my CPH2197 using Tapatalk

    Comment

    • GCE
      Platinum Member

      • Jun 2017
      • 1473

      #3
      On a rewire you need to adhere to the latest regulations same way that if you installed a need circuit it would need to be done correctly .

      You cannot sign off a rewire under

      As Dylboy pointed out reg 6.12.1.3 needs to be followed