    Bosal to PVC

    Gents, what's the best way to join new pvc conduit to bosal?

    Sent from my SM-A226B using Tapatalk
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #2
    I usually add an adaptor to it at the bottom to then go over the Bosal. But hoping there is a better practice to it perhaps ?

    Sent from my CPH2197 using Tapatalk

    Comment

    • Andrew_van_Zyl
      Bronze Member

      • Mar 2022
      • 131

      #3
      Originally posted by Dylboy
      I usually add an adaptor to it at the bottom to then go over the Bosal. But hoping there is a better practice to it perhaps ?

      Sent from my CPH2197 using Tapatalk
      Ah yes. Perfect! Many thanks

      Sent from my SM-A226B using Tapatalk

      Comment

      • Dylboy
        Gold Member

        • Jun 2020
        • 777

        #4
        Awesome !

        Looks like you on the same job as me currently haha, re-wiring old house to get rid of the VIR (material ) cable

        Sent from my CPH2197 using Tapatalk

        Comment

        • GCE
          Platinum Member

          • Jun 2017
          • 1473

          #5
          Does a bosal adaptor male not fit the conduit with 2 lock nuts - You could then use an earth tag to earth the conduit .

          On a hash and bash I normally remove all steel conduit as it is normally rusted and or about to start rusting and burst the plaster work

          Comment

          • Isetech
            Platinum Member

            • Mar 2022
            • 2274

            #6
            Just be careful of that dust in the ceiling space, it is lethal. Dont be a hero, wear a mask.
            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

            Comment

            • Dylboy
              Gold Member

              • Jun 2020
              • 777

              #7
              You are right ! I need to get more. Thing is I buy it for the guys and one for my self, as time goes they lose it or break it and even my one gets lost.... anyway I need to get more.

              I even get a bunch of the white mask ones, a bunch in a packet, all of a sudden it's all "used".

              Anyway it's a cost factor that needs to be applied. As well as some form of accountability

              Sent from my CPH2197 using Tapatalk

              Comment

              • Andrew_van_Zyl
                Bronze Member

                • Mar 2022
                • 131

                #8
                Originally posted by GCE
                Does a bosal adaptor male not fit the conduit with 2 lock nuts - You could then use an earth tag to earth the conduit .

                On a hash and bash I normally remove all steel conduit as it is normally rusted and or about to start rusting and burst the plaster work
                Picked up a couple of these at Liteglo. Pricey but im being anal. Thanks for the reminder wrt dust masks

                Sent from my SM-A226B using Tapatalk

                Comment

                • Andrew_van_Zyl
                  Bronze Member

                  • Mar 2022
                  • 131

                  #9
                  Originally posted by Dylboy
                  Awesome !

                  Looks like you on the same job as me currently haha, re-wiring old house to get rid of the VIR (material ) cable

                  Sent from my CPH2197 using Tapatalk
                  Ya I'm a 59 year old ceiling rat

                  Sent from my SM-A226B using Tapatalk

                  Comment

                  • Dylboy
                    Gold Member

                    • Jun 2020
                    • 777

                    #10
                    Ah good ideas, I will also use that adaptor, as GCE says you can then do an Earth ring.

                    You at the liteglo braamficher? That is my local supplier too.

                    Sent from my CPH2197 using Tapatalk

                    Comment

                    • Isetech
                      Platinum Member

                      • Mar 2022
                      • 2274

                      #11
                      Dont forge tthe brass bush.
                      Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                      Comment

                      • GCE
                        Platinum Member

                        • Jun 2017
                        • 1473

                        #12
                        Originally posted by GCE
                        Does a bosal adaptor male not fit the conduit with 2 lock nuts - You could then use an earth tag to earth the conduit .

                        On a hash and bash I normally remove all steel conduit as it is normally rusted and or about to start rusting and burst the plaster work
                        Should have added that you need to put a brass bush on as well to stop the sharp edges - You get a female one
                        You also get a pvc one but down this side not always easy to get

                        Comment

                        • Isetech
                          Platinum Member

                          • Mar 2022
                          • 2274

                          #13
                          So let's clear up a few things, now I am really showing off my old age.

                          You get old 16 mm split metal conduit, which would most likely have old VIR wiring, unless on a really, really, tight budget, remove completely and replace.

                          Then you get the old 20 mm black conduit, which would normally have a thread on the end of the pipe, unless you extend it with steel conduit and use a steel threaded coupling or adapter with the correct locknuts and bushes to maintain the earth continuity used in old systems with 2 wires, using the old metal lumex plug sand switches or the crabtree metal plug and cover, you going to need to make alternate earthing arrangements.

                          Then you get the galvanized steel conduit for coastal regions (within 20 km of the sea), as above applies.

                          I have found the best way to maintain the earth is to run a new earth wire, however, as we all know the budget controls everything, so you need to make a plan.

                          I have found that a piece of sandpaper, a bonding strap and a roofing screw and cold galv spray, will get the best results.

                          You sand the metal pipe to clean it and remove any paint or rust, wrap the copper bonding strap around the pipe , use an M5 brass nut washer and screw to secure the copper strap to the pipe, connect the earth wire to the new earth wire or another steel conduit using the same method ( not ideal, but a budget quick fix), then spray the strap with cold galv (if on the coast to prevent corrosion).

                          Then you take a piece of off cut wire, fit a lug and using the roofing screw to secure the lug to the old steel 4x4 or 4x2 box, then attach it to the earth terminal and check continuity.

                          DON'T REPLACE OLD METAL SOCKET OUTLETS WITH PLASTIC SOCKET OUTLETS AND ONLY CONNECT THE RED AND BLACK WIRE, JUST BECAUSE THERE IS NO EARTH WIRE DOESNT MEAN NO EARTH IS REQUIRED. IT MEANS THE OLD STEE LCONDUIT IS USED AS THE EARTH CONTUNUITY CONDUCTOR. (If you dont know this you shouldn't be working on electrical installation and at the same time, tell your boss he should spend less time playing at the toy shop and more time supervising his unskilled teams on site)
                          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.