    High earth loop

    Hello : )

    First time since going my own I have a property with a high loop, 4.15ohms.

    Is it the client to phone the power supplier to sort or is it up to me ?

    As I see it the client needs to do it but what is the consensus of who calls the power supplier ?

    I assume the fix they would do is to make it a TNC-S as it is TNS so they just add a large cable to join the neutral and earth.

    Old old property, bought in 2015 where the CoC for that sale the oke put in infinity symbol for the reading. So I assume been bad for a long time !

    A few things on it is just wrong so not worth the paper as usual but still need to get it sorted.

    Sent from my CPH2197 using Tapatalk
  • Thys LOW Elektries
    Silver Member

    • Jan 2021
    • 269

    #2
    Normally they put a bridge between the earth and the neutral, easy cheap, and legal
    We have a kiosk on the outside of the houses where the council's supply comes in.
    We just put a bridge between the neutral and the earth stud inside the kiosk and the problem is sorted out
    TNC-S systems are old and we are phasing it out, replacing it with the TNS system.

    Comment

    • Dylboy
      Gold Member

      • Jun 2020
      • 777

      #3
      Yes ya I assume so and seen it before l. Basically make a TNS and TNC-S.

      Thing is with this is the TNS will be converted to TNC-S. Not sure of all the pros and cons other than on a TNC-S if the neutral is lost or becomes high restsitance a shit ton of current flows through the earth cables and plumbing and metal fittings.

      Wish I could get a paid for bursary and become and electrical engineer hahaha then I may have some answers haha

      Sent from my CPH2197 using Tapatalk

      Comment

      • Thys LOW Elektries
        Silver Member

        • Jan 2021
        • 269

        #4
        The problem started in the early 60's with the use of a 4-wire system, it was very common and cheap, mainly for 3-phase equipment with no earth.
        They brought the cable to a kiosk, without an earth, in the kisok they bridge everything to create an earth.
        Only later did they realise it might work good in a factory or comercial building but not in a house.