Yip we at it again, I know I said I was going to take a break, but if the customer wants the customer gets.
So we are busy with a 8 kw single phase with a bunch of panels and a 12 kw with even more panels.
8 kw, easy peezey, I can do them with hangover in the morning and be done by lunch time.
However the 12 kw is rather interesting:
Max DC input power = 15600W
PV input voltage 550VDC (160 VDC - 800 VDC)
MPPT range = 200 Vdc -650 Vdc
PV input current = 26 Adc + 13 Adc
No of mppt trackers 2
Number of strings 2+1
The Dc is not the same as the single phase units.
Dont be fooled by the 12 KW, its actually only a 4kw x 3 (18 amps, which isnt much). I almost got caught with this, lucky I downloaded the manual and read it.
18 amps per phase is not much, considering it will be connected to single equipment, there is not much you can load onto it, just the same stuff.