Aircon circuit

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Andrew_van_Zyl
    Bronze Member

    • Mar 2022
    • 131

    #1

    Aircon circuit

    Gents,
    Domestic aircon unit trips earth leakage. Should it be on ELU in the first place?
    TIA
  • Isetech
    Platinum Member

    • Mar 2022
    • 2274

    #2
    I would fix the tripping problem, the only reason the ELU trips is because there is a problem or faulty.

    IF the aircon is plugged into a socket outlet, yes.

    IF the aircon is connected to a weathe rproof isolator outside next to the unit, no.

    Like I said if the earth leakage units trips touch, if you bypass the ELU, ther eis a risk that "you" create a dangerous environment, best you check everything and verify the metal parts are not live before you leave, otherwise you could get yourself into a spot of trouble.

    Originally posted by Andrew_van_Zyl
    Gents,
    Domestic aircon unit trips earth leakage. Should it be on ELU in the first place?
    TIA
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

    Comment

    • Thys LOW Elektries
      Silver Member

      • Jan 2021
      • 269

      #3
      Had a similiar issue with an aircon, finally we found a leek on the drain pipe that drips water on the motor which caused the trip. Good luck with finding the fault.
      All advice I can give is not to remove the aircon from the earth leakage

      Comment

      • ACElectric
        Junior Member
        • Oct 2023
        • 17

        #4
        NO

        Comment

        • Gene
          Full Member
          • Jan 2019
          • 40

          #5
          Normally an a/c circuit is a dedicated supply and not on the E/L, unless it is plugged in a plug circuit then must surely be on an E/L?