Are you a over night solar installer or a qualified electrician why not see if you can fix the problem?Another case, did the E loop and the N loop of a Victron.
E loop of 4.6ohms
N loop of 4.6 ohms.
This means the resistance of the earth wire was the same as the Neautral thus the same readings.
This gives a fault current of 49.3 Amps (the voltage was 227on the rest instrument)
So now that means the output CB needs to be at minimum a 25Amp CB to satisfy the double the current thing as that allows instant trip. (Depending on the type or curve of the breaker).
But the AC passthrough is 70Amps! So putting a 25A main CB basically renders the inverter useless.
So now what happens when it comes to the CoC when we test the inverter supply ?
Sent from my CPH2197 using TapatalkComment
-
You may think you are " Die Sparky " but for a first post without knowing the guys and value that they bring to this forum , I think you have overstep the mark.
If you have no value to add , rather keep quite , otherwise please explain the reason that both readings would be the sameComment
-
Both readings should be the same or very close because you are testing the loop either via the neutral or via the earth but they should be much lower. Posible cause for high readings i dont think has to do with electronics i believe there has to be a neutral earth bonding relay/contactor so mabe loose connections or bad contacts.You may think you are " Die Sparky " but for a first post without knowing the guys and value that they bring to this forum , I think you have overstep the mark.
If you have no value to add , rather keep quite , otherwise please explain the reason that both readings would be the sameComment
-
The AC passthrough is 70 amps but can the inverter deliver 70 amps in island mode? Would have to be one hell of a inverter so perhaps 4.6 ohm is correct for the inverter?Comment
-
-
Valid point
Think we are over thinking
Dylboy is taking readings in island mode which would mean sizing the output CB of the inverter but we have all been thinking back to incoming CB
The incoming readings under the incoming CB , being 70Amps, would need to be tested to determine the size for that CB
Will let Dylboy confirm my thought process .Comment
-
A point to remember here. All inverters have a built in Electronic over current detection. Trying to size a CB after the inverter in my opinion is fruitless, as it will trigger long before any circuit breaker will even experience an over current, and in my opinion is merely a circuit isolator more than a circuit breaker.
In the case that the electronics fails with in the inverter, it in most cases will be a short circuit.
2 things may happen, either the incoming supply circuit will trip due to the short within the inverter, or the ELU may trip due to their being an earth fault due to the failure.
In the case that there is a failure in the battery circuit, then the in line battery protection fuse nay blow, alternatively if it is a Lithium then the BMS will disconnect the battery from the battery line.Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.zaComment
-
Interesting thread, brothers.
So basically, it's pointless having a passthrough capability of 70A when the inverter can only deliver say 20A in islanding mode.
Am I correct in saying that the essential load must be selected so that it should not exceed the islanding mode capability of the inverter ?
ie. Forget about what the pass through capability is when deciding on the essential load.Comment
-
I would say yes, as there is a relay in the unit which is probably the rating of the inverter. Exceeding the inverter current would probably trip the inverter even in pass through mode, as I have had my inverter bleeping when power through the inverter starts nearing the inverter capacityInteresting thread, brothers.
So basically, it's pointless having a passthrough capability of 70A when the inverter can only deliver say 20A in islanding mode.
Am I correct in saying that the essential load must be selected so that it should not exceed the islanding mode capability of the inverter ?
ie. Forget about what the pass through capability is when deciding on the essential load.Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.zaComment
-
Yip - I agree with JustloaditInteresting thread, brothers.
So basically, it's pointless having a passthrough capability of 70A when the inverter can only deliver say 20A in islanding mode.
Am I correct in saying that the essential load must be selected so that it should not exceed the islanding mode capability of the inverter ?
ie. Forget about what the pass through capability is when deciding on the essential load.
Problem is contractors/installers are using bypss current in the design when placing complete houses on inverters and telling owners to switch appliances off and limit load just before loadshedding starts .
In the real world that is never really successful and they all forget the unknown power outage that happens , besides the fact that regulations do not allow it .Comment
-
Would still be nice to see a circuit breaker and a fuse though.A point to remember here. All inverters have a built in Electronic over current detection. Trying to size a CB after the inverter in my opinion is fruitless, as it will trigger long before any circuit breaker will even experience an over current, and in my opinion is merely a circuit isolator more than a circuit breaker.
In the case that the electronics fails with in the inverter, it in most cases will be a short circuit.
2 things may happen, either the incoming supply circuit will trip due to the short within the inverter, or the ELU may trip due to their being an earth fault due to the failure.
In the case that there is a failure in the battery circuit, then the in line battery protection fuse nay blow, alternatively if it is a Lithium then the BMS will disconnect the battery from the battery line.Comment
-
Wow pvc conduit bends so much nicer if you dont bend it over the knee. Just grab it like big motorcycle handles and bend it. Also nothing makes my loose my cool more than when the wires to a socket is way too short and when the back box is like 100mm away from the socket😡Comment
-
Just a question regarding your statement about regulations not allowing it.Yip - I agree with Justloadit
Problem is contractors/installers are using bypss current in the design when placing complete houses on inverters and telling owners to switch appliances off and limit load just before loadshedding starts .
In the real world that is never really successful and they all forget the unknown power outage that happens , besides the fact that regulations do not allow it .
All I can find is in 7.12.2.4 that states that there must be an automatic disconnecting device should the capacity of the alternate supply be exceeded.
I take it that the circuit breaker on the output of the inverter will suffice.
Am I missing something else in the regs ?Comment
-
In my opinion a circuit breaker installed after the inverter/alternative supply is already a given under 16.6.1 for isolation and also under 6.7 , protection
What I read in this particular reg is that the supply is not overloaded causing a change in voltage or frequency outside of normal.
That the parts of the installation that may cause an overload are automatically disconnected before any fault/tripping can occur - On bigger installations we use contactors or motorized CB to take out aircons , refrigeration so as not to overload the generator .
Coming back to a domestic install with an inverter you would need to ensure that either the essential D/Board is sized correctly for the inverter or if you feeding the complete installation that the higher loads are dropped out with a contactor automatically so that you are not relying on homeowner to run around and make sure heaters , dishwashers , geyser , stove etc are switched off before load shedding so as not to overload the inverter.
If you rely on homeowner to drop the loads , what happens in an unexpected power outage ? it will trip the unit and the chance of voltage dropping out of spec first is high.
Bear in mind that this reg also stands on 800Kva alternative supplies that could take awhile to trip the CB
In short - overload protection is a given this is on top of the overload protection.
7.12.2.4 Where the alternative supply is intended to provide a supply to an
installation that is not connected to the main supply, or to provide a supply as
a switched alternative to the main supply, the capacity and operating
characteristics of the alternative supply shall be such that danger or damage
to equipment does not arise after the connection or disconnection of any
intended load as a result of the deviation of the voltage or frequency from the
standard range. Means shall be provided to automatically disconnect such
parts of the installation, as may be necessary if the capacity of the alternative
supply is exceeded.Comment

Comment