E Loop and inverters

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Derlyn
    Platinum Member

    • Mar 2019
    • 1748

    #31
    Now that's what's so lekker about this forum. Thank you GCE.
    Much appreciated.

    Enjoy the weekend.

    Comment

    • Shadyshaun
      New Member
      • Nov 2023
      • 8

      #32
      What is pass through capability?

      From the grid to the inverter, including the UPS and charge capacity, OR

      The solar capacity to charge the battery and charge the battery, OR

      A combination of both, OR

      The current which can passthrough the relay to the UPS output, when not in islanding mode?




      Originally posted by Derlyn
      Interesting thread, brothers.

      So basically, it's pointless having a passthrough capability of 70A when the inverter can only deliver say 20A in islanding mode.

      Comment

      • Shadyshaun
        New Member
        • Nov 2023
        • 8

        #33
        "edit - The solar capacity to charge the battery and charge the battery, OR"

        The solar capacity to charge the battery, supply the UPS output and feedback to the grid? There seems to be some confusion, with regards to pass through current

        Comment

        • Dylboy
          Gold Member

          • Jun 2020
          • 777

          #34
          Hello : )

          Been following the thread but no time to really reply.

          But today I had the chance to use a Fluke multi function tester. The very cool one that does it all.

          Anyway I used my majortech earth loop tester thingy, blue and handheld.

          With my one testing another Victron install I got 3.80ohms (somewhere there) on the earth loop.

          I then used the fluke MFT and I got 1.2 (again somewhere there)...

          So now I am wondering if my meter struggles with the inverter supply in determining the values.

          We then tested the grid supply and both meters pretty much the same with a .1 or so difference.

          Unfortunately it was not the install of where this thread was created but still something to consider with regards to readings.


          Now it's time to find the R50odd thousand for a MFT...

          Also side note tried the Earth loop tests at sockets with the no trip function and it worked amazingly !

          Sent from my CPH2197 using Tapatalk

          Comment

          • Dylboy
            Gold Member

            • Jun 2020
            • 777

            #35
            My understanding of pass through is it is the amount of amps that can go through the inverter, it's internals will manage the battery charge depending on the load.

            So let's say 50A max pass through, it will take in 50Amps to distribute to load and if their is any excess power to then charge the battery. So of the laid is 40Amps the excess of 10A will be used to charge the battery.

            Sent from my CPH2197 using Tapatalk

            Comment

            • Derlyn
              Platinum Member

              • Mar 2019
              • 1748

              #36
              Originally posted by Shadyshaun
              What is pass through capability?

              From the grid to the inverter, including the UPS and charge capacity, OR

              The solar capacity to charge the battery and charge the battery, OR

              A combination of both, OR

              The current which can passthrough the relay to the UPS output, when not in islanding mode?
              From all the discussions I've had and the research I've done, I understand the pass through current to be the AC current that can be delivered from the grid, through the inverter relay when not in islanding mode.

              Comment

              • Dylboy
                Gold Member

                • Jun 2020
                • 777

                #37
                Originally posted by Derlyn
                From all the discussions I've had and the research I've done, I understand the pass through current to be the AC current that can be delivered from the grid, through the inverter relay when not in islanding mode.
                Yes ya agreed with that it is only when grid is available.

                Sent from my CPH2197 using Tapatalk

                Comment

                Working...