Same conduit for plug and stove

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Mlb
    Junior Member
    • Feb 2024
    • 14

    #1

    [Question] Same conduit for plug and stove

    Hi

    I am redoing the kitchen and installing new plugs. Is it allowed to have the oven's neutral, live and earth wire running through the same conduit as another plug socket that is right next to the isolator switch? The plug will obviously have its own live and neutral but share the same earth wire as the stove.
  • GCE
    Platinum Member

    • Jun 2017
    • 1473

    #2
    What size stove circuit ?

    It is not good practice and you will be pulling 2 circuits through one box either the plug or stove isolator and would need to label accordingly

    Sharing the earths is not a good idea as , rather have separate complete circuits.

    Comment

    • Mlb
      Junior Member
      • Feb 2024
      • 14

      #3
      It's an electric oven with a gas Hob. No electric stove. I don't have the oven specs on me at the moment but I don't see it drawing more than 16 amps (if not much less). On either side of the isolator is a plug socket. To avoid chasing 2 additonals channels for each plug I thought I could just run a twin earth cable through the same conduit. The plugs will be fed via twin earth cable directly from the plugs breaker. Oven will be fed with loose live, neutral and earth from the 'stove' breaker/isolator. There is enough space in the conduit

      Comment

      • Die sparky
        Full Member
        • Nov 2023
        • 25

        #4
        Originally posted by Mlb
        It's an electric oven with a gas Hob. No electric stove. I don't have the oven specs on me at the moment but I don't see it drawing more than 16 amps (if not much less). On either side of the isolator is a plug socket. To avoid chasing 2 additonals channels for each plug I thought I could just run a twin earth cable through the same conduit. The plugs will be fed via twin earth cable directly from the plugs breaker. Oven will be fed with loose live, neutral and earth from the 'stove' breaker/isolator. There is enough space in the conduit
        Are you sure there is enough space in the conduit i believe it should not be filled more than 40%

        Comment

        • ACElectric
          Junior Member
          • Oct 2023
          • 17

          #5
          Hi----This is the only calculation approved by the chief inspector to do what you want to do---The 40% is a requirement for cables in wireways.--- See the following regs and tables regarding conduit sizes and wires inside it. It is relatively simple.



          Click image for larger version

Name:	cable sizes conduit.jpg
Views:	1
Size:	49.4 KB
ID:	266309Click image for larger version

Name:	conduit size wires.jpg
Views:	1
Size:	36.1 KB
ID:	266310Click image for larger version

Name:	wireway conduit sizes.jpg
Views:	1
Size:	36.6 KB
ID:	266311

          Comment

          • skatingsparks
            Silver Member

            • Mar 2008
            • 375

            #6
            In the same conduit - Yes - if its big enough

            If you have 2 x 6mm GP (L+N for stove) and 3 x 2.5mm (C.P.C. for stove and L+N for socket) + 1.5mm (for socket C.P.C.) you are at 96 (max 90 on C value on 20mm conduit)

            I have seen where guys use manufaturers data and calculate CSA of all cables in conduit and and they still have 40% space - don't like it but have seen it to justify why they passed it.

            Same earth condutor for 2 circuits - in a new instal - I'd say no.
            In an existing (old) install where your not modifying anyhthing - i believe its a pass (don't like it but....)

            If it was already there, I wouldn't make a client rip thier wall apart to change it.