Eskom contact to sort high Earth loop

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #16
    No CoC issues yet, the Eskom guy said as the installation ok and that it's Eskom side means i could issue the CoC.

    I have not done so as yet and planning to try meet up to show him the results and then they get it sorted.

    What this shows me is there is no more care about what is right and anything and everything can be in a grey area to pass blame.

    Sent from my CPH2197 using Tapatalk

    Comment

    • Isetech
      Platinum Member

      • Mar 2022
      • 2274

      #17
      Back to the earthing arrangement, chances are they will just bridge the neutral and earth on the pole or in the CDU, depending on the supply and place you live this could also be dangerous.

      We log a fault and email the danger notice to the supplier and the user/owner attach the notice to the COC and move on.

      There is being negligent and there is taking steps to attempt to do the right thing.

      You could go the route Derlyn suggested, with an earth spike, this could start costing a few bob.
      Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.