Welcome to The Forum SA. As a visitor you have read only access to the public content areas of this website. You will have to register as a member to access all content, post messages and network with our members. Membership is free and registering is quick and easy. You can click here to register now and become a member within minutes.
I dont know 3 phase inverters.
Dave mentioned that a 12Kw 3phase inverter consists of 3 single phase 4Kw inverters.
Now the question is, what is the phase voltage of each 4 Kw inverter ? 220v or 380v ?
It is 3 phase inverter but you can draw single phase supplies of each phase and if balanced then 4kw on each phase , most allow up to 70% imbalance on the phases
These are 2 pics of the inverter screen running on grid in parallel
On the load side under one with a tong tester I get 25amps and on the other 14 amps
How is it possible that the load power can be higher than the grid power ? I would have expected the grid to be slightly higher than the load on all 3 phases..
How is it possible that the load power can be higher than the grid power ? I would have expected the grid to be slightly higher than the load on all 3 phases..
The grid power consumption is slightly higher than the load power consumption.
One curiosity is the power draw is similar on both inverters, but the current on one is nearly double the current reported on the other.
The grid power consumption is slightly higher than the load power consumption.
One curiosity is the power draw is similar on both inverters, but the current on one is nearly double the current reported on the other.
Slightly ? - grid shows 25Amp on one inverter which should be around 5Kw and yet it show +/-1 and the 2nd inverter 14 Amps which should show +/-3Kw yet both show 1 Kw
I thought CT's were in wrong position but when we ran off grid it started the confusion
Slightly ? - grid shows 25Amp on one inverter which should be around 5Kw and yet it show +/-1 and the 2nd inverter 14 Amps which should show +/-3Kw yet both show 1 Kw
I thought CT's were in wrong position but when we ran off grid it started the confusion
I was looking at the on-grid-supply power numbers. Looks like there's a 100w overhead on each inverter according to the power report.
I agree the current reports raises red flags - properly.
I was looking at the on-grid-supply power numbers. Looks like there's a 100w overhead on each inverter according to the power report.
I agree the current reports raises red flags - properly.
Yip and that is where I come back to the KW readings on inverter not matching actual draw
The inverter picks up the current, total , at +/-38 amps which is what I get on the combined load
The total grid power( 3 pases added together) is higher than the load, but there are individual phases where the load power exceeds the grid power. That's what I was referring to.
Another question. You said there are 4 escalators if I'm not mistaken. Does each inverter feed 2 escalators or do both inverters , in parrallel, feed all 4 escalators ?
The total grid power( 3 pases added together) is higher than the load, but there are individual phases where the load power exceeds the grid power. That's what I was referring to.
Another question. You said there are 4 escalators if I'm not mistaken. Does each inverter feed 2 escalators or do both inverters , in parrallel, feed all 4 escalators ?
Inverters are in Parallel and supply all 4
Discrepancy on phases can be motor loads and power sharing between phases - You often find 1 phase on a motor drawing less and that is generally due to incoming powerfactor - Can be as much as 10% in extreme cases
How about the phases on the one inverter (the one with the high current readings) are wired incorrectly?
My read is the evidence suggests the power draw readings are the most likely to be reasonably accurate. (DC draws off the battery - both in current and SOC after a couple of hours, one inverter fairly close to 3kW across all measures).
So what could cause a massive current discrepancy in a star supply to delta load situation?
In a rig installed by an IT guy.
On a supply with a phase rotation that runs the wrong way (compared to the rest of the country).
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.