    Good day, I have been asked to design a sub-db for a 3phase grid tie inverter system, that only works when Eskom works.
    So far in the main DB, I have an Eskom main breaker that supplies power to the inverter sub-db and an inverter breaker that receives power from the inverter sub-db.
    In the Inverter sub-db, I have an Eskom main breaker, an Inverter main breaker, and surge arrestors for Eskom and the Inverter.
    I had also thought of including LED indicators for Eskom and the inverter power.
    What else needs to be in the Inverter sub-db?

    The pv contractor will do the PV installation and electrical work on his side and then just have to hook his system up to our network

    Any advice would be welcome
  • GCE
    Platinum Member
    • Jun 2017
    • 1495

    #2
    Is the system str grid tie , no Batteries ?

    It sounds like it - then all you need is a surge arrestor on main incoming and a CB feeding the inverter , no sub DB needed .

    Inverter will have a CT that will be on the main incomer to monitor usage and stop feed back , if needed

    Comment

    • Thys LOW Elektries
      Silver Member

      • Jan 2021
      • 269

      #3
      The only reason I was thinking of a sub DB is to give the PV installer a place where they can disconnect the power safely when they need to work cause they don't have a key to gain access to the main db. Also one can isolate the supply safely before the inverter is installed

      Comment

      • GCE
        Platinum Member
        • Jun 2017
        • 1495

        #4
        Originally posted by Thys LOW Elektries
        The only reason I was thinking of a sub DB is to give the PV installer a place where they can disconnect the power safely when they need to work cause they don't have a key to gain access to the main db. Also one can isolate the supply safely before the inverter is installed
        If there is distance from the DB then you would need to have an isolator at the inverter that they can use to switch off

        Comment

        • Thys LOW Elektries
          Silver Member

          • Jan 2021
          • 269

          #5
          Yip, a distance, plus the main DB is in a service shaft that is not visible from where the inverter is installed.
          When you say Isolator, do you mean something like a CBI 4x4 60Amp three-phase isolator or do you mean a 4-pole Isolator in a DB?

          Comment

          • GCE
            Platinum Member
            • Jun 2017
            • 1495

            #6
            Originally posted by Thys LOW Elektries
            Yip, a distance, plus the main DB is in a service shaft that is not visible from where the inverter is installed.
            When you say Isolator, do you mean something like a CBI 4x4 60Amp three-phase isolator or do you mean a 4-pole Isolator in a DB?
            I would put a 4 pole CB in the DB and a normal isolator , waco/ crabtree isolator next to the inverter - On a str grid tie , as soon as grid drops then the inverter switches off - It needs grid as it follows the grid / sync with grid

            Comment