    DB Extension.

    Came across the following yesterday.

    18 way surface DB became too small when 2 air cons were added to the installation, so another 8 way DB was installed next to it to house the 2 air con mcb's
    and labelled " Main DB Extension" and containing only 2 single pole mcb's. ( No main breaker etc. )

    The question is,........ Can this added small DB be seen as part of the main db or must it be seen as a seperate DB with it's own double pole main breaker etc.

    When doing a COC, do I include 2 test reports or 1 ?
  • GCE
    Platinum Member
    • Jun 2017
    • 1482

    #2
    I would say it is a sub DB and needs a main isolator and labeled as Sub DB 1 - 2nd test report would be needed then

    Comment

    • Derlyn
      Platinum Member
      • Mar 2019
      • 1756

      #3
      Thanks GCE. I actually thought it was quite a novel way of increasing the size of the db. I have quoted on doing exactly as you suggested. Thank you.