    Battery fuse protection

    On an inverter installatuon, must the positive and negative from the battery be protected by a fuse or is it sufficient for only the positive to be fused ?
  • GCE
    Platinum Member
    • Jun 2017
    • 1490

    #2
    Originally posted by Derlyn
    On an inverter installatuon, must the positive and negative from the battery be protected by a fuse or is it sufficient for only the positive to be fused ?
    Generally , Yes , on PV type inverters and battery systems - There are exceptions which are/were found in Telecoms situations where the neg battery terminal was earthed then you only fused positive or if positive was earthed then negative fused - Think railways do a similar thing were positive is overhead and the rails are negative and earthed -

    7.12.7.5 In addition it shall be recognised that the supply from each inverter,
    battery arrangement and PV panel (or identified clustered group), constitutes
    a supply, and requires arrangements similar to point of supply, which shall
    include switch-disconnection arrangements and shall comply with 7.12.5.


    7.15.1.3 The live polarity is the polarity that is not connected to earth (positive
    on a negative-earth system, or negative on a positive-earth system); the earth
    or "0 V" polarity is the polarity that is connected to earth.

    Comment

    • Derlyn
      Platinum Member
      • Mar 2019
      • 1763

      #3
      Thank you GCE.

      I notice 7.15.4.1 states that where one of the polarities is connected to earth, all the switch-disconnectors and protective devices shall break the live polarity only. The return circuit shall not be disconnected or broken.

      Now one will have to determine if the negative terminal of the battery is internally earthed to the casing before deciding on whether to fuse the negative or not, because we earth the battery casings.

      Comment

      • GCE
        Platinum Member
        • Jun 2017
        • 1490

        #4
        Originally posted by Derlyn
        Thank you GCE.

        I notice 7.15.4.1 states that where one of the polarities is connected to earth, all the switch-disconnectors and protective devices shall break the live polarity only. The return circuit shall not be disconnected or broken.

        Now one will have to determine if the negative terminal of the battery is internally earthed to the casing before deciding on whether to fuse the negative or not, because we earth the battery casings.
        Battery systems bought for PV have no negative earth - Inverters will throw out all sorts of alarms - It is only exceptional circumstances and have only ever seen it in the Old analogue telephone systems and railways