    Load Readings

    Hi I wonder if I am posting in the correct forum ,if by chance I am not then would some- one please be kind and direct me to the correct forum my query being as follows
    I have 3 clip on current meters ( tong testers ) and when a load is measured I get different readings now all is very well if one just wants to check if a circuit is drawing a load , but when one has to explain the reason for the different readings ,
    Meter A is a analogue meter
    Meter B is a digital “ R.M.S. “ meter
    Meter C is a digital meter
    On an inductive load the readings are
    A = 43 amps B = 42 amps C = 45 amps
    On an resistive load the readings are
    A = 95 amps B = 87.5 amps C = 103 amps
    What could the reason be for the different readings.
    Thanks Mike.
  • murdock
    Suspended

    • Oct 2007
    • 2346

    #2
    if you swop b and c does the 103 amps more to b?

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #3
      Are all the clamps 'hall effect'? Are any of the clamps of the flexible type? It would be helpful if you could give make and model numbers of all the equipment you're using.