The following mentions flexible cords which the definition describes 4mm or smaller, or am I misunderstanding this definition?
6.1.11 [I]Where flexible cords are used as part of the electrical installation[/I], the
selection, installation and colour identification (see 6.3.3) shall be done in
accordance with this part of SANS 10142. Flexible cords with cross sectional
area less than 1 mm2
shall not be permitted.
6.1.12 Where flexible cords are used, the strands of the conductors shall be
mechanically protected with ferrules to prevent the strands from being cut off
in terminations.
The definition of a flexible cord is as follows
3.8.2
flexible cable
cable of which the conductors consist of strands of diameter not
exceeding 0,51 mm and of which the insulation and covering are such that
they afford flexibility and in which the nominal cross-sectional area of each
conductor exceeds 4 mm˛
3.8.3
flexible cord
cable of which
a) the nominal cross-sectional area of each conductor does not exceed
4 mm˛, and
b) each conductor consists of strands of diameter less than 0,31 mm
My understanding of this is that cord (cabtyre) of 2.5mm with fine wire is allowed. Or am i missing something?
However, SANS does have amp ratings for flexible cables but not for flexible cords. Not sure why
in terminations.
3.8.2
flexible cable
3.8.3
flexible cord
cable of which
4 mm˛, and