cable sizes
  • bergie
    • Sep 2010
    • 308
    cable sizes
    anybody know where to get tables for working out cable ratings.
    i have to quote on a 850 amp supply. it is in a trench most of the way and 52m long.
    i normally have to phone aberdare in joburg. the technical guy worked it out to 3x 240mm 4 core armoured cables.seems a bit of an overkill.would work out to over R 160 000 just for cable.
  • murdock
    • Oct 2007
    • 2346
    if it is underground in a trench i also get 3 x 240mm
    i am sure you know this already...but just watch the fault levels when selecting equipment and cables for that matter...
    i did a project last year and was advised by everyone to use parallel cables but due to the fault level calculated at the 200 kw motor we had to use 1 x 185.
    • mikilianis
      • Dec 2008
      • 124
      The fault levels do you mean p.s.c. or am I on the wrong path