bathrooms and fixed appliances

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • murdock
    Suspended

    • Oct 2007
    • 2346

    #1

    bathrooms and fixed appliances

    what are the regulations with regards to a mirror with lights in a bathroom in lets say zone 2...100 mm away fron the shower without a door.

    if you have an extractor fan directly above your shower which regulations would you take note of...if the extractor is connected to the light fitting and is above 2.5 metres from ther shower basin...what is the zone just above the shower and what if it is extracting the steam?
  • murdock
    Suspended

    • Oct 2007
    • 2346

    #2
    even better still...what about a fixed appliance mounted at 2.6 m above the shower basin if the shower rose is 2.1 metres above the shower basin? which regulation to use?

    Comment

    • bergie
      Email problem

      • Sep 2010
      • 308

      #3
      if you have an extractor fan directly above your shower which regulations would you take note of...if the extractor is connected to the light fitting and is above 2.5 metres from ther shower basin...what is the zone just above the shower and what if it is extracting the steam?
      i wouldnt worry about the fan as the motor is in the ceiling area and the housing is plastic.if its extracting steam ,its not going to extend the zone,as its not as if the steam is flammable. if its connected to the light then the light switch should be double pole.
      Last edited by Dave A; 17-Jun-11, 05:25 AM. Reason: format help

      Comment

      • murdock
        Suspended

        • Oct 2007
        • 2346

        #4
        Originally posted by bergie
        i wouldnt worry about the fan as the motor is in the ceiling area and the housing is plastic.if its extracting steam ,its not going to extend the zone,as its not as if the steam is flammable. if its connected to the light then the light switch should be double pole.
        or on earth leakage

        Comment

        • TECHNICIAN 810
          Junior Member
          • Jun 2011
          • 19

          #5
          All bathroom appliances including mirror lights should be on earth leakage.
          It's allso regulation to have ceiling fans on earth leakage.

          Comment

          • murdock
            Suspended

            • Oct 2007
            • 2346

            #6
            Originally posted by TECHNICIAN 810
            All bathroom appliances including mirror lights should be on earth leakage.
            It's allso regulation to have ceiling fans on earth leakage.
            in which zone?

            Comment

            • Sparks
              Gold Member

              • Dec 2009
              • 909

              #7
              Table 7.1 ― Conditions under which electrical equipment
              may be installed in a bathroom
              1 2 3 4
              Conditions that apply in
              Electrical equipment Zone 1 Zone 2 Zone 3
              Distribution and control X X Normal provisions of this
              part of SANS 10142
              Bell push B1 and C1 B1 and C1 Normal provisions of this
              part of SANS 10142
              Socket-outlet X C2 Normal provisions of this
              part of SANS 10142
              Wall switch X X Normal provisions of this
              part of SANS 10142
              Pull switch Normal provisions of this part of SANS 10142
              Distribution boards X X X
              Fixed appliances
              (including luminaires)
              (A and B1)
              or
              (B2)
              (A and B1)
              or
              (B2)
              Normal provisions of this
              part of SANS 10142
              The symbols used in this table are the following:
              A denotes that earth leakage protection shall be provided;
              B1 denotes that the equipment shall be so enclosed in insulating material that it is not
              possible to touch current-carrying parts with the standard test finger;
              B2 denotes that class II appliances shall be used;
              C1 denotes that the equipment shall be supplied from a safety supply with a secondary
              voltage not exceeding 25 V;
              C2 denotes that the equipment shall be supplied from a safety supply that has a
              maximum rating of 50 VA. Shaver supply units shall comply with SANS 61558-2-5/
              IEC 61558-2-5 (SABS IEC 61558-2-5).
              X denotes that the equipment shall not be installed.
              Amdt 1

              7.1.4.3.1 In zones 0, 1 and 2, no switchgear and accessories shall be
              installed except that emergency push buttons, which operate at a safety
              extra low voltage at nominal voltage not exceeding 12 V, are permitted in
              zones 1 and 2.

              Zone 1 is limited by
              a) the vertical plane circumscribing the outer edge or 0,20 m from the
              inner edge (where the ledge is too wide) of the bathtub, shower basin,
              or for a shower without a basin, by the vertical plane 0,60 m from the
              shower rose,

              Comment

              • Sparks
                Gold Member

                • Dec 2009
                • 909

                #8
                In other words, neither the fan nor the lights are acceptable.
                Maybe Dave can get the table to display correctly.
                Pasting is a whole lot faster than I can type.

                Comment

                • murdock
                  Suspended

                  • Oct 2007
                  • 2346

                  #9
                  zone 1-2 only extend to 2.5 m which means at 2.6 m it is out of the zone 1 and 2...zone 3 rules apply.

                  Comment

                  • Sparks
                    Gold Member

                    • Dec 2009
                    • 909

                    #10
                    Almost but not quite, it extends to "at least 2500mm" and then must be read with "600mm above the shower rose".

                    Comment

                    • murdock
                      Suspended

                      • Oct 2007
                      • 2346

                      #11
                      Originally posted by Sparks
                      Almost but not quite, it extends to "at least 2500mm" and then must be read with "600mm above the shower rose".
                      where did you find that?

                      because we were discussing this issue last week...something else came up...what if the shower rose is 2600mm...just to put a spanner in the works...and yes anything is possible.

                      Comment

                      • Sparks
                        Gold Member

                        • Dec 2009
                        • 909

                        #12
                        7.1.2.2 Zone 1
                        Zone 1 is limited by
                        a) the vertical plane circumscribing the outer edge or 0,20 m from the
                        inner edge (where the ledge is too wide) of the bathtub, shower basin,
                        or for a shower without a basin, by the vertical plane 0,60 m from the
                        shower rose, and
                        b) the horizontal plane 2,5 m above the bathtub or shower floor.
                        And then Figure 7.1.3

                        If the rose is 2.6m afl your zone is extended to 3.2m

                        Keeping in mind that we are in the new SA
                        I have come across plenty who did not consider the "600mm above the rose".

                        Comment

                        • murdock
                          Suspended

                          • Oct 2007
                          • 2346

                          #13
                          thanks for for that info.