Earthing
  • TECHNICIAN 810
    • Jun 2011
    • 19
    Earthing
    Is the earthing of guttering, down pipes and metal roofing still compulsory
    when the main supply cable is underground? Or is this only applicable for overhead supply installations.
    Another question, most of the new plumbing pipe is plastic or pollycarb, so then it is not necessary to earth all taps anymore.
  • murdock
    • Oct 2007
    • 2346
    you would need to look at the application...but you are on the right track...if the overhead line has been replaced with airdac or an underground cable the requirements would change.
    you cant earth plastic...but also look at the installation as a whole because in some cases the hot water pipe is still copper...but if the cold is plastic then you cannot bond the geyser.
    • TECHNICIAN 810
      • Jun 2011
      • 19
      Thanks Murdock, the application is actually the world class developer Century property developments. None of the houses on the entire estate have earthing on gutters or taps, all piping is poly C, nor are the DB boards labled DB 1 Fed from.....
      Sub Street boxes are numberd and labled.
        • 4927
        If the plumbing pipework is all polycop then you can't bond the pipework and I wouldn't bond the taps. As far as I know though polycop (orange pipe) isn't rated for hot water use but I would check this with a plumber.
        If necessary, running an earth bond to the roof or gutters should be easy as all new developements require an earth bar in the loft for other services so you should be able to run a wire from that for gutters, roof, TV antenna, satalite dish etc.
        • bergie
          • Sep 2010
          • 308
          if its not an overhead supply then its not necessary to earth the gutters or roof.
          what are the specs of the earth bar in the roof? a 2,5mm wire with a bolt through the rafter?
          i see cobra make this white polycop that can be used for hot water .very thick wall and very easy to work with.
          • Leecatt
            • Jul 2008
            • 409
            This is the only thread for earthing so I would like to use it for my example.
            Went to a house yesterday where the guy was getting shocked when touching the gate motor bracket, fridge and anything else "earthed"
            There was no municipal earth supply but I found a connection to an earth spike from the earth bar and a second connection between earth and neutral, seems ok?
            Well it is as long as neutral is neutral but in this case the municipal supply had been reversed and the neutral was now live. Seems the earth spike was not as effective as required and the house was alive.
              • 4927
              What was the earthing arrangement, TN-C-S, TT? Can you post a couple of photos? What earth impedances did you test?
              First question is why didn't the RCD (earth leakage breaker) in the DB trip?
              Are you sure the supply was reversed? It's not a common fault...in fact it would reek of saboutage or willful damage. Also with an incoming supply reversal the live supply would be directly to the earth rod as well as any other parallel earth paths through the building services etc so the second question is why didn't the MCB in the council cabinet trip?
              Are you sure it wasn't a high resistance or missing supply neutral rather than a complete supply reversal?? This could also cause many the symptoms you describe.
              To receive a shock from the chassis of an appliance you need multiple faults to occur simultaneously. (1)There is an insulation fault that allows a leakage current to flow between the live conductors and the chassis. (2)The earthing is inadequate which allows the chassis touch voltage to rise. (3)The RCD is faulty
              • Leecatt
                • Jul 2008
                • 409
                It had me stumped as well for an hour or so.
                The E/L tested at 25mA ok, but did not trip unless the button was pushed.
                I disconnected the incoming supply completely and had 220v between live and neutral, 220v between neutral and earth and nothing between live and earth.
                All I can conclude is that the earth rod is not effective and I cannot say why the E/L did not trip
                • bergie
                  • Sep 2010
                  • 308
                  just a thought, assuming the spike passes at 20 ohms,if there is direct live on to it you would only have 11 amps.not enough to trip the main switch.if there is a good suppliers earth the current should be more. so the spike might be fine.
                    • 4927
                    Yep, if it was a TT installation and there were no parallel paths through the bonding to other services then a 20 ohm spike wouldn't be sufficient to trip the MCB on the incoming power. You'd need an earth impedence of less than 3 ohms. That said I've never seen a domestic installation on a TT earthing arrangement but it might be because I rarely work domestic and only in my area.
                    The worrying thing for me is the incoming supply reversal. This should never happen under any circumstances.
                      • 22812
                      Not that long ago we had to go out to a house with a three phase supply where all hell had broken loose. Turned out there had been a cable theft, and the municipality had crossed the neutral with a phase when replacing the cable.
                      Actually, I wonder how their claim against the municipality went? I probably should give them a call.
                        • 4927
                        I've seen a few rough installations done by the council and Eskom but thankfully I've never heard of this happening. Anyone doing the same with a 1000Amp commercial supply would only do it once. On the rare times I've not been happy with something and logged a complaint they've always made good and in reasonable time.
                        I've seen damaged cause on three phase systems by a 'missing' neutral fault. When the neutral is allowed to float it's voltage follows the highest loaded phase so single phase equipment on the other two phases receives 380volts. It can cause a lot of damage to appliances.
                        • bergie
                          • Sep 2010
                          • 308
                          i've heard of a few times where council have connected 380 volt to a single phase supply. they have insurance ,so they pay quick. incidentally today someone told me that there neighbour who didnt have power for a while(smallholding) had there power reconnected this week and a lot of electronic appliances were blowing up. smoke coming out of the dvd player,etc. i told them to report it to eskom straight away.
                          re the earthing:there are quite a few overhead supplies still around in the older parts of cape town.there wouldnt be a supplied earth,only the spike.
                            • 4927
                            I assumed there might be from some of the fault descriptions I've seen posted. My experience of domestic installations is very little. When no earth is supplied then the spike impedence values are critical, also a nice deep spike is essential for sseasonal stability.
                            Ths made me smile because it reminded me of an audio clip called 'Melk Boer' someone emailed me a few years ago. It was a recording of a melk boer who phoned Eskom with a complaint about his motors being trashed by the power linesmen workng on a power pole. I'll see if I can find it.
                            *Edit* Link (not family friendly...you've been warned!!!!)
                            • Phillip Armstrong RTB
                              • Apr 2023
                              Is there anything such as an Earthing Certificate? I have an Engineer asking for Earthing Certificates for various office buildings that fall under his care. As far as I know it is not a requirement to earth steel roofs if the supply is an underground cable. I agree that all Earth Bonding is necessary ( Geysers; steel light fittings; etc. ) As for the normal COC the Earth Loop test and Neutral Loop test would be done.