NH Fuse between 48V Battery and Inverter

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • MPAD
    New Member
    • May 2023
    • 5

    #1

    [Question] NH Fuse between 48V Battery and Inverter

    Is this fuse suitable for 48V DC between battery and inverter? Will it extinguish the dc arc? It's being sold as battery fuse at retailer. I've installed it but am now questioning whether it is correct. The AC690V seems to be highlighted.

    Click image for larger version

Name:	Chint80AEdit.jpg
Views:	1
Size:	15.3 KB
ID:	270048
    Click image for larger version

Name:	MyChint.jpg
Views:	1
Size:	25.5 KB
ID:	270049

    Other fuses that are sold as battery fuses also don't have DC on it?

    Click image for larger version

Name:	GC.png
Views:	1
Size:	71.4 KB
ID:	270050
    Click image for larger version

Name:	Jean.jpg
Views:	1
Size:	16.6 KB
ID:	270051
  • Isetech
    Platinum Member

    • Mar 2022
    • 2274

    #2
    Regardles sof what you read on social media or what the wholesaler tells you, its always better to go to the product site and download the data sheet and certtificates for products.


    CHINT is a globally renowned leader in smart energy solutions, offering the most comprehensive product ranges across the whole industrial chain, from Plant to Plug.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

    Comment

    • Isetech
      Platinum Member

      • Mar 2022
      • 2274

      #3
      You will notice in the certificate that all the fuses are AC and DC rated, you will notice some of the DC voltage ratings are half the AC voltage rating. The fault levels are also less.

      So when someone says the fuse is not DC rating refer to the certificate.

      Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

      Comment

      • MPAD
        New Member
        • May 2023
        • 5

        #4
        I did check the website overview and certificate initially,

        the problems were
        1. the picture on the website does not match the model I have
        2. the overview says AC690 and the certificate has DC250 (also certificate is not in english)

        I have also asked Chint Global and they have responded from regional person of Africa
        "
        Thanks for your attention to CHINT.

        We do not have fuse for DC48V application
        "

        Comment