    If you installed a solar system in 2023, I would be interested to see how your ROI is going.
    It would be interesting to compare a 5 kw (R100- 150 K to an 8 kw R150 - R250K if installed in 2023)
    I did a few calculations using actual data collected from installed units, and the results are rather interesting.
    Looking at it realistically (a system with 12 panels) , I would say if all goes well and the price of electricity keeps going at the current rate, and no additional fees are added to the bill, it might just even out the cost in about 12 - 15 years.
    Looking at it from a convenience point of view, the value of the system has already paid for itself 10 fold.
    However when we look at the amount of grid failures and the duration of these grid failures, the load shedding system is currently just not suitable. Looks like we are going to be be going back to adding generators to keep lights on, or laying out thousands on batteries, which are great if we have sunny days.
    • 1473
    Not sure how you getting to 12 to 15 years
    I have looked at various systems that we have installed and depending on Qty of batteries come in at between 5 and 8 years
    Standard 5kw system with 5kwh battery we are seeing 22K a year savings .If I take the 22k and add 10% for increases every year it is 4 years and 100K is saved . We seeing 3K bills come down to R700 and likewise bills that are up at 4K mark down to R700 .
    Where bigger battery systems have been installed we see R0 bills coming in but the pay back period inc due to the cost of batteries
    • Tradie
      • Feb 2025
      • 329
      It's the figure people are using, 10 year warranty for an inverter/battery combo, one of the reasons we only install combo unit with a 10 year warranty. Our oldest unit is only 3 years old, are they going to last 10-15 years, only time will tell.
      The last of the older Axpert units that we installed, have been replaced, Many of them have had PCB issues, you hear a bang and puff of smoke and you in for a board replacement, we dont bother anymore, just replace. We only have a few FLA batteries in trolley type inverters, which will be replaced with a drop in lithium battery.
      Dont you install Victron units, which batteries do you install?
      • Tradie
        • Feb 2025
        • 329
        How do you figure out the ROI and savings?
        • Tradie
          • Feb 2025
          • 329
          Let do a quick calculation for 2023, using some data collected, no feedback. I am not aware of any customers who have had the correct meter installed, only a notice to inform the customer that it is illegal to feedback electricity into the grid.
          Solar cost to purchase and install (with a COC) 8 kw system with 2 batteries and 12 x 545 watt panels - R210 000 (average cost in 2023)
          PV - 1997.3
          Load - 3884.9
          Export - 2.6
          Import - 5923.3
          Discharge - 1110
          Charge - 1310
          Using the scale 4 as for the example, without complicating the calculation we will just use the 2023-2024 tariff R2.97 (it will make the roi look better)
          If we divide the total by 12 to get an average monthly bill - 5923.3 kwh/12 = 493.61kwh
          The average bill should be around R1466.02 per month.
          The savings would be the PV generated ?
          1997.3/12 = 166.44 kwh per month
          166.44*2.97 = R494.33 per month.
          How much ROI for the solar installation and savings on the bill, less the council registration, PR engineer, TOU tarrif and monthly council fee?
          • Tradie
            • Feb 2025
            • 329
            What sort of budget do we need to consider when installing solar?
            Initial outlay for a system -
            1 x 8 kw inverter R28 000
            2 x 10 kwh batteries R35 000
            18 x 550 watt panel R28800
            Total excluding all the its and pieces = R91800.00
            Plus bits and pieces = R120 000 ( a rough estimate)
            Council registration, including COC and PR engineer and new meter installation = ?
            Tariff upgrade to TOU = ?
            Monthly additional cost added to your monthly council account = ?
            Feedback tariff = ?
            Am I missing anything ?
              • 1473
              We see the average house hold above 500 units a month , generally around 700 units
              PE , we have 3 prepaid meter tariffs , first 250 units ( R 3.08/kwh) , 2nd 250 units ( R3.66/kwh) and the the rest ( R 4.05/kwh) so anybody over 500 units starts saving quickly .
              We don't need engineer sign off and the 4 quadrant meter comes in at +/-R7K
              Monthly charge on a 4 quardrant TOU with feedback is Monthly charge R104.34 +vat SSEG support charge R 52.17 + vat = Total inc Vat R 179.99
              I was on prepaid ( with solar fitted) and cost was around R700 per month , just had meter fitted and now down at R 300 per month inc TOU and monthly charges
              Savings on first year was R 22 304.40 while on solar meter - Reckon if I had TOU I would have had savings of R29K
              Had a client make a statement over a beer that there is no way he will ever break even on his system - 5KW panels , 8Kw Deye 15Kwh Weco 5k3 batteries - Did a quick calc and got a savings of R 27K year 1
              He would be looking at 7 years with 10% per year increase - Last year in PE we effectively had 16% inc on first 500 units and then 12,5% on the balance
              Also just had TOU meter fitted - He has dropped his Bill further as the majority of import is at night on off peak at R1,66/kwh vs the lowest prepaid tariff at R 3/kwh
                • 1473
                Take the units consumed for the month - Work out what it would have cost in prepaid without solar - minus what it costs with solar = savings
                Have attached a sheet that I used to do a quick calc
                • Tradie
                  • Feb 2025
                  • 329
                  This is a prepaid installation, with solar installed, using 2024 per kwh rate (R2.976)
                  PV - 1997.3
                  Load - 3884.9
                  Export - 2.6
                  Import - 5923.3
                  Discharge - 1110
                  Charge - 1310
                  Monthly average bill is 5923.3/12= 493.58kwh per month
                  493.58 kwh per month x R2.97 = R1465.93 loaded into the meter per month.
                  Solar generated average per month 1997.3/12 = 166 kwh (used)
                  166 x 2.97 = R493.02
                  R493.o2 x 12 = R5916.24 saving per year.
                  Cost to install R220 000/R5916.24 = 37 years to pay back the initial cost at this rate, this excludes registration costs, monthly utility fees, PR engineer and all the other little costs, like maintenance panel cleaning, maintenance inspections, etc,etc.
                  It would be great if we could get meters to feedback and optimise the system.
                  The customer has requested more solar panels, however the data collected shows its not a solar panel issue, there is plenty power not being utilised during the day, it's a storage issue (TOU), adding more batteries to utilise the power during peak hours (6-9 pm and 4-7 am) , when the most power is used, would be the best way to reduce the bill. The system idles from 9 am once the batteries are fully charged.
                    • 1748
                    At the end of the day, installing solar is more about convenience than saving money.
                    If one uses the money that would have been used to install solar on money making ventures, a lot more can be made than the savings that having solar will offer one.
                    If one takes the money saved on the electricity bill seen as a percentage of the cost of installing the system, it is clear that installing solar is a dumb idea if saving money is the sole motivation of the project. That money can be put to better use.
                    As I said, it's all about convenience and it is my opinion that this ROI talk is only sales talk.
                    • Tradie
                      • Feb 2025
                      • 329
                      If you installed a load shedding solution, then I would agree with you 100 %, in fact most load shedding solutions are just bottomless money pits. I have a load shedding solution, I switch it off until we have power issues.
                      I also agree with your comment about it being for convenience, why have an endless money pit when you can optimise the system to create some form of return or at least save on your electricity bill?
                      Just remember not everyone lives in a single room with a candle and a gas stove, some people run their business from home, some want the convenience of switching on the tap for a hot shower every night (we live in the 21 century) , or need the security for the property, or what may seem like a silly thing to others, opening the gate remotely could save your life or at least reduce the risk of being hijacked at the gate.
                      If eskom could provide a stable power supply we wouldn't be having this discussion, the reality, billions have been spent, why not optimise your system?
                      • Tradie
                        • Feb 2025
                        • 329
                        Lets look at the numbers from the inverter, some figures randomly taken from an inverter
                        PV - 325.7
                        Load - 885.7
                        Export - 102.1
                        Import - 707
                        Discharge - 17.7
                        Charge - 27.3
                        The PV produced is 325.7 kwh for the month, which has to be split because the exported kwh is a lot less than the used kwh
                        For example 325,7kwh - 102.1 kwh = 223.6 kwh
                        The export rate in our hood is only R1.25, compared to the tariff R2.97
                        Export value - 102.1 x 1.25 = R127.62
                        the solar used is far more valuable - 223.6 x 2.97 = R664.09
                        Imported - 707 x 2.97 = R 2099.79
                        the charge and discharge value
                        27.3 - 17.7 = 9.6 kwh
                        • Tradie
                          • Feb 2025
                          • 329
                          Bill from the utility - import 707 kwh
                          707 kwh x R2.97 = R2099.79
                          The saving would be the PV used plus the PV exported
                          PV used = PV total less the PV exported
                          325.7 kwh - 102.1 kwh = 223.6 kwh
                          223.6 kwh x R 2.97 = R664.09 (tariff rate)
                          102 kwh x R1.25 = R127.5 (export rate)
                          Total saving = R664.09 + R127.50 = R791.59 per month
                          • Tradie
                            • Feb 2025
                            • 329
                            Just when you thought, great my system is optimised and my system is saving me R 791.59, this is not an average, it is the best month of the year, then you have to subtract the initial cost of the system, including all other stuff, like registration, the maintenance cost, monthly utility fees.
                            Total saving for the year R791.59 x 12 = R9499.08 per year (it is less than this but we being optimistic today and it was designed a sa load shedding solution, not focused on ROI)
                            System cost R120 000.00
                            R120 000/R9499.08 = +/- 12 years.
                              • 1473
                              You are not allowing for a 10% increase per year in Elec pricing which effectively works to an extra 10% saving per year
                              You would then be looking at between 8 and 9 years
                              Year 1 9,499.08
                              Year 2 10,448.99
                              Year 3 11,493.89
                              Year 4 12,643.28
                              Year 5 13,907.60 57,992.83
                              Year 6 15,298.36
                              Year 7 16,828.20
                              Year 8 18,511.02 108,630.42
                              Year 9 20,362.12 128,992.54
                              Year 10 22,398.33
                              Year 11 24,638.17
                              Year 12 27,101.98
                              Total 203,131.02
                              Cost of Purchase 120000