  • CLIVE-TRIANGLE
    Gold Member

    • Mar 2012
    • 886

    #31
    The EPS is no good as a UPS, it switches too slowly. So the UPS as expected does go to it's battery. However I would have thought the once the EPS has switched, it would be happy. Alas no.

    Dave, the EPS is a modified wave form, so perhaps that's why.

    Once this happens the downstream UPS will switch back to normal mode if it is happy with the power that's being delivered to it by the upstream UPS.
    That is what is not happening.

    Comment

    • Justloadit
      Diamond Member

      • Nov 2010
      • 3518

      #32
      So when the battery of the UPS is flat, then the EPS will continue maintaining power for the duration of the charge of the EPS, should not be a problem then, until power is returned..
      Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
      Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

      Comment

      • CLIVE-TRIANGLE
        Gold Member

        • Mar 2012
        • 886

        #33
        Originally posted by Justloadit
        So when the battery of the UPS is flat, then the EPS will continue maintaining power for the duration of the charge of the EPS, should not be a problem then, until power is returned..
        That's what I was hoping for, but it doesn't happen. I have even disconnected the supply from the EPS to the UPS, then reconnected. It's simply as if it's not there. The other devices, not connected to the UPS but to the second outlet on the EPS, work fine. Could it be that the UPS rejects the modified sine wave of the EPS?

        Comment

        • AndyD
          Diamond Member

          • Jan 2010
          • 4946

          #34
          That is the most likely possibility, the 'modified sine' output of the EPS is not up to scratch. You could try reversing the UPS and EPS so that the EPS is downstream but if the output of the EPS is poor quality I'm not sure if this would have adverse effects on the items it's running.
          _______________________________________________

          _______________________________________________

          Comment

          • Justloadit
            Diamond Member

            • Nov 2010
            • 3518

            #35
            Andy, not necessarily, today's equipment are made with SMPS, to maintain low cost, which work of a DC signal. The internal feedback loops with in the UPS, adjust the PWM, so that the voltage required by the equipment is maintained, this is the reason that a SMPS is rated between 95-265V. These SMPS's will work with a pure DC signal, so the fact that the supply is a modified sine wave will have no effect on the equipment. The incoming supply is first inserted through a bridge rectifier to convert to a pure DC signal, which it then uses to supply the equipment.

            The only time that a "pure" sine wave is required, is when there are inductive loads involved, such as an electric motor, be it a fridge, pool pump, water pump, microwave, fluorescent lights which use a starter and a choke, very cheap LED lamps which use RC as part of it's PSU.

            TVs, decoders and most modern printers will work quite happily with a modified sine wave.

            The reason that inductive loads and motors require a sine wave is due to 2 reasons, the first being that the square peak of the incoming wave is on for too long, which causes the iron in the motor to overheat because the motor was designed for a shorter peak. The 2nd reason, is the rise time from zero to peak is vertical, which changes the characteristics of the inductor filter circuit and excessive current will flow causing overheating.
            Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
            Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

            Comment

            • CLIVE-TRIANGLE
              Gold Member

              • Mar 2012
              • 886

              #36
              Then I'm back to square 1.

              Comment

              • Dave A
                Site Caretaker

                • May 2006
                • 22810

                #37
                Can you post the make and model number of the UPS, Clive?
                Participation is voluntary.

                Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                Comment

                • Justloadit
                  Diamond Member

                  • Nov 2010
                  • 3518

                  #38
                  I would follow AndyD's idea, of placing the EPS after the UPS.
                  So Power fail, UPS continues till battery flat, then EPS continues from there. When power returns, UPS battery charges, EPS battery charges, and load supplied by mains.
                  Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                  Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                  Comment

                  • AndyD
                    Diamond Member

                    • Jan 2010
                    • 4946

                    #39
                    Originally posted by Justloadit
                    Andy, not necessarily, today's equipment are made with SMPS, to maintain low cost, which work of a DC signal. The internal feedback loops with in the UPS, adjust the PWM, so that the voltage required by the equipment is maintained, this is the reason that a SMPS is rated between 95-265V. These SMPS's will work with a pure DC signal, so the fact that the supply is a modified sine wave will have no effect on the equipment. The incoming supply is first inserted through a bridge rectifier to convert to a pure DC signal, which it then uses to supply the equipment.

                    The only time that a "pure" sine wave is required, is when there are inductive loads involved, such as an electric motor, be it a fridge, pool pump, water pump, microwave, fluorescent lights which use a starter and a choke, very cheap LED lamps which use RC as part of it's PSU.

                    TVs, decoders and most modern printers will work quite happily with a modified sine wave.

                    The reason that inductive loads and motors require a sine wave is due to 2 reasons, the first being that the square peak of the incoming wave is on for too long, which causes the iron in the motor to overheat because the motor was designed for a shorter peak. The 2nd reason, is the rise time from zero to peak is vertical, which changes the characteristics of the inductor filter circuit and excessive current will flow causing overheating.
                    What you say is true but a power supply with active PFC and/or harmonic filters will often run warmer if the power is modified sine. This may or may not be an issue. Realistically, as you say, it's unlikely the appliance will suffer immediate damage unless is poorly designed in the first place but the lifespan of the device could be shorter running on a modified sine supply due to the higher component temperatures.
                    _______________________________________________

                    _______________________________________________

                    Comment

                    • CLIVE-TRIANGLE
                      Gold Member

                      • Mar 2012
                      • 886

                      #40
                      Originally posted by Dave A
                      Can you post the make and model number of the UPS, Clive?
                      Click image for larger version

Name:	eps ups.png
Views:	1
Size:	26.6 KB
ID:	264493Click image for larger version

Name:	ACDC Page 92.jpg
Views:	1
Size:	58.5 KB
ID:	264494
                      MEISSNER XT1200 (1200VA) UPS _ TVR Computers.pdf

                      The EPS is the 2000 B model

                      Comment

                      • wynn
                        Diamond Member

                        • Oct 2006
                        • 3338

                        #41
                        I have decided for the time being I will start work later when the shed is from 6 to 8AM.
                        I will have a long lunch when it is from 12 to 2PM.
                        I will knock off early when it is from 4 to 6PM

                        Otherwise I will just grin and bear it.
                        "Nobody who has succeeded has not failed along the way"
                        Arianna Huffington

                        Read the first 10% of my books "Didymus" and "The BEAST of BIKO BRIDGE" for free
                        You can also read and download 100% free my short stories "A Real Surprise" and "Pieces of Eight" at
                        http://www.smashwords.com/books/view/332256

                        Comment

                        • ians
                          Diamond Member

                          • Apr 2010
                          • 3943

                          #42
                          Now you getting smart. It would be interesting to hear what legal implication this would have with regards to the labour laws.
                          Comments are based on opinion...not always facts....that's why people use an alias.

                          Comment

                          • DanE
                            Junior Member
                            • Apr 2015
                            • 17

                            #43
                            I do the same thing at my factory, as long as you don't work them longer than the standard weekly hours or eliminate their break times but merely shift them then you are in the clear. Easiest is to work it over a week duration and ensure staff work their 40 and you give them their 5. Aside from groaning and moaning which you'll have to endure, your in the clear.


                            Sent from my iPad using Tapatalk

                            Comment

                            • Justloadit
                              Diamond Member

                              • Nov 2010
                              • 3518

                              #44
                              If I am not mistaken, and I stand to be corrected on this, employers can send staff home in the case of load shedding with out paying those hours. There is a minimum of 4 hours of wages that must be paid though.

                              The real issue here is productivity. If you are a manufacturer and depend on getting product out to invoice, then this can really kill any profit you make, as the efficiency drops dramatically.
                              Certain expenses remain in place, such as rent, rate and taxes, insurance, telephones, loans, HP, lease etc.
                              Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!