    Fridge not running on generator, invertors but only on grid

    Maybe someone can shed some light on this one.

    Yesterday the street muni transformer blew (IMHO due to no oil change in 8 years and very hot weather) leaving us with no grid electricity. So after a 6 hours I decided to start the three phase generator (with each phase servicing a specific single phase section of the house) to get the fridge and freezer cold again. The fridge (which is a brand new Bosch KGN36XI32 with power demand of 160W) simply refused to start up on the generator supply. That I could understand as the wave form on the phase is a bit dirty.

    So I switched the fridge supply to the standby 400W Victron sine wave inverter with a 2,5mm2 lead. Now the fridge's internal light came on, the touch control panel worked but the compressor did not start. At full load demand the fridge should start up ... not the case. So I pulled a spare 1,5kW Meanwell sine wave inverter out. Now the fridge's internal light works, but the touch control panel only randomly and the compressor refused to start.

    OK, my logical deduction is the fridge went with the transformer to electrical heaven. A nice way to start Christmas.

    After 12,5 hours a new transformer was installed and grid supply was reinstated. Let me try again I told the Boss, and she just laughed.

    Low and behold, plug Mrs Fridge in and there she starts up and purrs away ....

    Can anyone shed some light on the reason why the grid supply works, but two pure sine inverters do not?
  • AndyD
    Diamond Member

    • Jan 2010
    • 4946

    #2
    Modern day appliances can be very complex devices with internal communications between different control boards and even between control boards and components and sensors. Sometimes the comms systems require a very low neutral earth voltage. The only thing I can think of is maybe a lack of N-E bond caused problems with the comms.
    _______________________________________________

    _______________________________________________

    Comment

    • mygoggie
      Full Member

      • Sep 2015
      • 76

      #3
      Thanks for the reply. That is one thing I have not thought of. Will measure and see if this is the issue!

      Comment

      • mygoggie
        Full Member

        • Sep 2015
        • 76

        #4
        You are spot on. The inverter(s) are V-0-V and there is a 70+V on N-E which the fridge does not like and will refuse to start. I did not realise the inverters were V-0-V so I now have a few decisions to make as I cannot connect these into my household circuits.

        Comment

        • Justloadit
          Diamond Member

          • Nov 2010
          • 3518

          #5
          Get a 600VA 1:1 ratio isolating transformer, primary side to the inverter and secondary side to the fridge. This will isolate the V-0-V issue.
          Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
          Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

          Comment

          • mygoggie
            Full Member

            • Sep 2015
            • 76

            #6
            It pays to buy quality inverters. Feedback from Meanwell is that it will auto sense V-0-0 downstream of the outlet and adjust the inverter's output to V-0-0. I will try this tomorrow in a controlled way.

            Comment

            • AndyD
              Diamond Member

              • Jan 2010
              • 4946

              #7
              Glad you're on the right track. If it's any consolation I like all the Meanwell devices I've come across, their power supplies and drivers are well designed, nicely manufactured, functional and they're reliable. I haven't worked with their inverters yet but hopefully they're equally good.
              _______________________________________________

              _______________________________________________

              Comment

              • mygoggie
                Full Member

                • Sep 2015
                • 76

                #8
                So our local Muni transformer blew up again and we were without grid power for a long time. I took the opportunity to get the fridge going on an inverter, but alas no go.

                This is what I did. I made sure the supply by the inverter to the fridge is V-0-0 and it only runs from a battery that is charged and coupled to another battery charger supplying a charge current at the same time.

                I took readings of the voltage between pins and these were L-N = 230V; N-E = 0V; L-E = 230V.

                As said before the inverter is a pure sine wave 1500W output with spiking loads up to 125% the 1,5kW for 10 sec. This is much more than the fridge will require.

                When connected and switched on, the fridge never tried to start. It just sat there doing nothing except shining the control panel lights.

                When the grid came on, plug the fridge into the wall outlet and off she goes, purring like a kitten.

                So the only thing left in my opinion is that the sine wave from the pure sine wave inverter is not to the liking of the fridge's controller.

                Any ideas???

                Comment

                • ians
                  Diamond Member

                  • Apr 2010
                  • 3943

                  #9
                  Try connecting other appliances to the inverter...kettle...drill etc and see what happens.
                  Comments are based on opinion...not always facts....that's why people use an alias.

                  Comment

                  • mygoggie
                    Full Member

                    • Sep 2015
                    • 76

                    #10
                    Originally posted by ians
                    Try connecting other appliances to the inverter...kettle...drill etc and see what happens.
                    And we have a winner ...

                    Now why would this make a difference as the inverter is not in sleep mode?

                    Comment

                    • smartappliance
                      New Member
                      • Jun 2024
                      • 2

                      #11
                      Fixes to Try
                      Check Wattage Make sure your generator or inverter can handle your fridge's starting wattage (higher than the running wattage listed on the label).
                      Upgrade Power:
                      Consider an inverter generator or a model designed for electronics.
                      If you're using an inverter, go for a larger one with more power.
                      Hard Start Kit: This can give your fridge's compressor the extra push it needs.
                      Check Wirin : Use thick extension cords and proper grounding to avoid voltage drop.
                      Call a Pro If you're still stuck, an electrician can test your setup and diagnose any problems.