Welcome to The Forum SA. As a visitor you have read only access to the public content areas of this website. You will have to register as a member to access all content, post messages and network with our members. Membership is free and registering is quick and easy. You can click here to register now and become a member within minutes.
Didn't even know there was another section hahaha.
If it is 12V and 100AH that is then 1200WH or 1.2KWH
Then if
24 V and 100AH that is then 2400WH or 2.4KWH
Is that correct ?
Sent from my CPH2197 using Tapatalk
That is correct -
Battery in parallel - voltage will be added , amp hour stays the same
In series - voltage stays constant , amp hours is added up
2 batteries in Series = ( 2x12v) x 100Amphr = 2 400Whr
2 in Parallel - = 12v x ( 2 x 100Amphr) = 2 400whr
As a quick rule I just use a 100Amphr battery using only 30% will give me 360w usable energy - If the client wants to run a 1 Kw load for 2 hours then I say he needs 2Kw of energy divide by 360W = 6 Batteries - The configuration of batteries to suit the inverter voltage all works out the same , The bucket of water is still the same size.
Awesome ! That is how I have done it and always understood it but had to make sure as the above stuff has me questioning my self. Albeit I did read it quick but still.
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.