    Earth Leakage

    Is an earth leakage faulty if it trips before or after the mA rating stipulated on the earth leakage?
  • Talmadge
    New Member
    • Apr 2013
    • 8

    #2
    I had this discussion with my electrician this morning. In my opinion it is definitely faulty if it trips after, as anything over 100 milliamps becomes lethal. It can also be faulty if it is too sensitive and trips around the 20 milliamps range, however not lethal, I think, it trips too quick and needs to be replaced. Any electricians out there that can shed some more light on this?

    Comment

    • bergie
      Email problem

      • Sep 2010
      • 308

      #3
      i think in sans it says 20 -30ma is acceptable. i need to go back and check.

      Comment

      • Pieter00
        Bronze Member

        • Mar 2013
        • 111

        #4
        Yes it is acceptable but would if the manufacturer standards stipulates 20mA on it, it must trip on that rating. But what if it doesn't. Even if it's a new earth leakage. Where is the fault?

        Comment

        • Talmadge
          New Member
          • Apr 2013
          • 8

          #5
          Is it tripping before or after?

          Comment

          • ians
            Diamond Member

            • Apr 2010
            • 3943

            #6
            The earth leakage is faulty if it doesn't trip after 30 Ma or if it trips when all the wiring is disconnected.
            Comments are based on opinion...not always facts....that's why people use an alias.

            Comment

            • Leecatt
              Silver Member

              • Jul 2008
              • 404

              #7
              Originally posted by Talmadge
              I had this discussion with my electrician this morning. In my opinion it is definitely faulty if it trips after, as anything over 100 milliamps becomes lethal. It can also be faulty if it is too sensitive and trips around the 20 milliamps range, however not lethal, I think, it trips too quick and needs to be replaced. Any electricians out there that can shed some more light on this?
              I had this problem last week, earth leakage and random tripping.
              I tested the unit with no load connected and found it was very sensitive and tripped at 21 Milli-amps.
              I found another unit that trips at 25 Milli-amps and the problem has gone now.
              By the way the acceptable range for any earth leakage unit is between 50% and 100% of its rating as indicated on the unit.
              For a modern home that would be between 15 and 30 Milli-amps
              To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

              Comment

              • ians
                Diamond Member

                • Apr 2010
                • 3943

                #8
                A common problem with random tripping, surge protection plug tops, they break down under load and cause random tripping.

                Another common problem, cut insulation on surfix, I have found insulation cut where the electrician strips the cable and doesn't use tape, it gets moisture in the cut and cause nuisance tripping.

                In fact there are so many, a good electrician will identify the problem and repair it and others will find other means to overcome the problem, bypassing a stove is one of the common remedies.
                Comments are based on opinion...not always facts....that's why people use an alias.

                Comment

                • Leecatt
                  Silver Member

                  • Jul 2008
                  • 404

                  #9
                  See
                  8.7.12 Operation of earth leakage units
                  To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

                  Comment

                  • Leecatt
                    Silver Member

                    • Jul 2008
                    • 404

                    #10
                    This house had various areas from where there were earth leakages. Some where electronic equipment, slight leakage at geysers and borehole pumps and various flourescent lights. Too many to mention here. Eventually it exceeded the 21 milliamps the earth leakage worked at or perhaps the unit had become more sensitive over time, and the only alternative was to raise the threshold of the earth leakage unit.
                    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

                    Comment

                    • Leecatt
                      Silver Member

                      • Jul 2008
                      • 404

                      #11
                      Originally posted by ians
                      A common problem with random tripping, surge protection plug tops, they break down under load and cause random tripping.

                      Another common problem, cut insulation on surfix, I have found insulation cut where the electrician strips the cable and doesn't use tape, it gets moisture in the cut and cause nuisance tripping.

                      In fact there are so many, a good electrician will identify the problem and repair it and others will find other means to overcome the problem, bypassing a stove is one of the common remedies.
                      This house had various areas from where there were earth leakages. Some where electronic equipment, slight leakage at geysers and borehole pumps and various flourescent lights. Too many to mention here. Eventually it exceeded the 21 milliamps the earth leakage worked at or perhaps the unit had become more sensitive over time, and the only alternative was to raise the threshold of the earth leakage unit.

                      It is incorrect to remove a stove from the earth leakage protected circuit unless it is connected via a "stove coupler"
                      See 6.16.3.3 Stove connection.
                      To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

                      Comment

                      • AndyD
                        Diamond Member

                        • Jan 2010
                        • 4946

                        #12
                        It's getting more and more common nowadays where the global cumulative leakage in a house exceeds the 20-30mA tripping threshold. Computers have an acceptable leakage of 1-3mA because of their built-in surge arrestors, same with many switch-mode power supplies like laptops, phone and battery chargers etc. Many people don't understand that the earth on majority of circuits is functional and not only there to prevent shocks through elevated touch voltages. Having a standing leakage of 10-15 mA isn't unusual and it doesn't leave much room for very minor fault currents that wouldn't otherwise be a problem.

                        Often the only solution is to spread the load through more than one RCD (earth leakage). Pretty soon each circuit should have its own RCBO which is a much better system than just one or two RCD's.

                        Click image for larger version

Name:	rcbo-cgd.jpg
Views:	1
Size:	22.9 KB
ID:	262157

                        RCBO's are still coming down in size and in price but it would be good practice to install them on the socket circuits if you can fit them in the DB.
                        _______________________________________________

                        _______________________________________________

                        Comment

                        • ians
                          Diamond Member

                          • Apr 2010
                          • 3943

                          #13
                          If the stove is connected to an isolator, there is no need to connect it to earth leakage (we don't use stove couplers in Durban) The only time you have to connect it to earth leakage is when the isolator has a combo isolator socket outlet, like we had in the old days.
                          Comments are based on opinion...not always facts....that's why people use an alias.

                          Comment

                          • ians
                            Diamond Member

                            • Apr 2010
                            • 3943

                            #14
                            Andy if anything I do believe in this country, I could see less being connected to the earth leakage rather than more earth leakage units being installed
                            Comments are based on opinion...not always facts....that's why people use an alias.