There is no substitute for experience.
I have a system that i use for finding an earth leakage fault.
Its very basic, but in most cases i solve the problem.
As in IANS post, which is self explanatory .
Unplug all appliances, turnoff underfloor heating, turn off pool (by their DP isolators)
Most of the time the fault is now cleared. Then i check each appliance out that was disconnected, i megger them out. I also systematically put the pool back on, then the UFH and so on.
Now if all is disconnected and isolated, then its a Neutral. Now i remove each neutral from the bar, and more often than not its the last one that is down to earth. I have already checked the lives and they are ok.
Cut a long story short i trace out and locate the problem eventually.
The other nuisance trip is a fridge, middle of the night it usually happens, this is usually a heater in the fridge getting moisture into it.
Some times i put the fridge on a dedicated circuit. hehee.
What i cant understand, and dont have the knowledge to make a comment is why some times the earth leakage works on a .2ohm when it should trip. Any thing less than 1 Meg ohm should in theory trip. ??
I have a system that i use for finding an earth leakage fault.
Its very basic, but in most cases i solve the problem.
As in IANS post, which is self explanatory .
Unplug all appliances, turnoff underfloor heating, turn off pool (by their DP isolators)
Most of the time the fault is now cleared. Then i check each appliance out that was disconnected, i megger them out. I also systematically put the pool back on, then the UFH and so on.
Now if all is disconnected and isolated, then its a Neutral. Now i remove each neutral from the bar, and more often than not its the last one that is down to earth. I have already checked the lives and they are ok.
Cut a long story short i trace out and locate the problem eventually.
The other nuisance trip is a fridge, middle of the night it usually happens, this is usually a heater in the fridge getting moisture into it.
Some times i put the fridge on a dedicated circuit. hehee.
What i cant understand, and dont have the knowledge to make a comment is why some times the earth leakage works on a .2ohm when it should trip. Any thing less than 1 Meg ohm should in theory trip. ??