  • debtcollectorZA
    Junior Member
    • Jun 2014
    • 14

    #16
    Pictures attached. If needs be I will attempt to open up the terminal box to get an idea of the wiring in there

    Click image for larger version

Name:	Loose Wires.jpg
Views:	1
Size:	28.6 KB
ID:	263061

    Click image for larger version

Name:	Terminal Box.jpg
Views:	1
Size:	38.4 KB
ID:	263062

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #17
      The wires could be for an internal thermal protective device or maybe even a dynamic brake. Maybe can you give the make and model number of the motor?
      _______________________________________________

      _______________________________________________

      Comment

      • debtcollectorZA
        Junior Member
        • Jun 2014
        • 14

        #18
        The plot thickens somewhat...
        I tested the current draw and 1.8Kw+ motor only draws 500w when running. Could the loose wires have something to do with the low current draw?

        Comment

        • bergie
          Email problem

          • Sep 2010
          • 308

          #19
          was it under load when you tested it. it wont draw more amps if it doesnt need to.
          the extra wires might be for a 2nd capacitor. sometimes there are 2 in parallel.

          Comment

          • AndyD
            Diamond Member

            • Jan 2010
            • 4946

            #20
            Originally posted by debtcollectorZA
            The plot thickens somewhat...
            I tested the current draw and 1.8Kw+ motor only draws 500w when running. Could the loose wires have something to do with the low current draw?
            How did you test the current? What instrument did you use? 500W isn't a current measurement it's a power measurement so I'm a bit confused about what you measured and how.

            Induction motors or squirrel cage motors are generally at their most efficient when they're under full load, if they're free wheeling (no load) they often draw around 25 or even 30% of their full load current even though they're just rotating free and doing no useful work. Likewise the power factor of a motor usually improves as the load increases.

            There's no hard and fast formula for off-load current draw, it very much depends on the individual motor but single phase motors have higher inefficiencies. If the saw was not actually cutting anything when you tested it then the power consumption of 500 watts would be expected.
            _______________________________________________

            _______________________________________________